Thanks, Chuck.

I talked with a former colleague that has a lot of experience in specing out 
UPS requirements (between battery-ready and generator-ready backups at the 
office they have up to 5 minutes of battery backup before the gas generator is 
needed with a 128-hour recharge time just to support their servers and wiring 
racks in the office).

He thinks that at 500W needed it would give me about 12 minutes on a 1400VA. My 
consideration is, then, give the server 2 minutes on battery. If full power has 
not been returned, shut down the server but leave the modem (w/ wireless) and 
switch running with power for up to 6 hours.

Now I need to build a server (looking at RAID5 8x2TB) for less than $1600 w/o a 
CPU if I can... a local custom builder quoted me $4000 today for a full system 
inc. CPU, RAM and DVD.

--
Ryan

On Aug 11, 2010, at 11:44 AM, Chuck Swiger wrote:

> Hi, Ryan--
> 
> On Aug 11, 2010, at 8:51 AM, Ryan Coleman wrote:
>> Total: 495W
>> 
>> According to a calculator if I enter all that information:
>> http://www.csgnetwork.com/upssizecalc.html
>> It says that it will use 693VA.
> 
> That sounds reasonable.  The better PSUs have "80 Plus" certification for 
> efficiency, and that's better than the typical wall warts used for modems and 
> switches and the like commonly manage.  (The efficiency they're assuming is a 
> bit over 70%; using 80% would be around 600VA.)
> 
>> Enter that into http://www.csgnetwork.com/batterylifecalc.html
>> It requires Amps... 495W  / 120 voltage = 4.125 amps... doesn't seem right 
>> but...
>> 192 hours... that's not right, right?
> 
> Assume for discussion their number was right.  In order to get 495W of output 
> load, the UPS needs to provide 693 volt-amps of juice to your equipment.  
> After the inverter and 10:1 stepup transformer used to convert 12VDC or 
> whatever the UPS batteries are charged to up to 120VAC, the current needed 
> would be 5.77 amps.  However, the 12VDC battery source itself would be 
> getting a draw of 57 amps (ideally; again, the inverter+transformer 
> themselves might only rate about 90% efficiency for very good quality UPS, so 
> would be drawing more like 60 or 65 amps).
> 
> A standard APC/Tripplite/whatever 700VA UPS tend so have a lead-acid battery 
> reasonably similar to a car battery, and typically will have around 100 
> amp-hours of charge; they'd probably give you 90 minutes of backup time.  But 
> you can look up the detailed specs of specific models and work from their 
> amp-hour (or watt-hour) ratings-- actually, I think I'm guestimating more 
> from what a 1200VA unit might provide, and a 700VA model is probably going to 
> provide more like 40-60 minutes of power...
> 
> Regards,
> -- 
> -Chuck
> 
> _______________________________________________
> freebsd-questions@freebsd.org mailing list
> http://lists.freebsd.org/mailman/listinfo/freebsd-questions