PowerWare has a UPS line with controlled outlets (up to 3 KVA)
Its is like a APC UPS and a Power switch, all for the price of a UPS
I think it has 4 independant outputs, so you can remotely power up/down 4
servers, all from the UPS software.

We use much larger models, 9150 15KVA with 3Phase input 1 phase output,
ideal to balance load on three phase
We also use the 9170 a 12KVA with n+1 redundancy
We use nti power switches behind the UPS

----- Original Message ----- 
From: "Charles Frolick" <[EMAIL PROTECTED]>
To: "Chris Ulrich" <IMail_Forum@list.ipswitch.com>
Sent: Thursday, December 30, 2004 9:35 PM
Subject: Re: [IMail Forum] OT: KVM over IP & RemoteReboot


> Hello Chris,
>
> Thursday, December 30, 2004, 12:38:57 PM, you wrote:
>
> CU> Sorry to go OT here, but with so many other hosts/ISPs you guys
probably
> CU> know this better than anyone and have dealt with it already....
>
> CU> We're adding about a dozen machines and want to start using KVM/IP and
> CU> equip these guys with remote reboot capabilities.
>
>
> If you already have a KVM Solution you can add this box
> http://www.realvnc.com/products/KVM-via-IP/.
>
> It will mean you don't throw away your current investment.
>
> CU> Second, we've about given up on a reasonably priced reboot solution.
Yes,
> CU> APC has managed powerswitches, but for us, we UPS each machine
> CU> so "pulling the plug" on one outlet (how the powerswitches reboot a
> CU> machine) is pointless because the UPS between the powerstrip and the
PC
> CU> keep it up.
> CU> I guess we could do one UPS followed by the powerstrip followed by the
> CU> servers, but what kind of UPS would you need to keep 8 mini-tower Dell
> CU> Poweredges
> CU> (300 or 400w PS) up and running?  Again, does that go over the top in
cost?
>
> I have run as many as 10 1U servers off of a single APC 1400, which
> works at 15 amps, and as many 24 off a single 20amp breaker split
> across 2 1400VA UPSs.  A 2200VA unit only needs a 20 amp circuit. What are

> you currently running them from? A single circuit breaker I bet, so
> all you really need is runtime, not power.  Buy a unit that matches
> the power rating of your current breaker, that has extended life
> battery add-ons, most brands have them.
>
> -- 
> Best regards,
>  Charles                            mailto:[EMAIL PROTECTED]
>
>
> To Unsubscribe: http://www.ipswitch.com/support/mailing-lists.html
> List Archive: http://www.mail-archive.com/imail_forum%40list.ipswitch.com/
> Knowledge Base/FAQ: http://www.ipswitch.com/support/IMail/
>


To Unsubscribe: http://www.ipswitch.com/support/mailing-lists.html
List Archive: http://www.mail-archive.com/imail_forum%40list.ipswitch.com/
Knowledge Base/FAQ: http://www.ipswitch.com/support/IMail/

Reply via email to