I’d recommend a battery test. Starting the test via the front panel should be 
sufficient, or you might be able to do it with upscmd.

This should let the UPS firmware discharge the battery a bit, and see how long 
it should last.

Conceptually, “OL LB” is not inconsistent- it means the UPS has AC power, but 
the battery state of charge is reading low (as might happen after the UPS 
restarts after an extended power failure) . You might have a CPS unit where the 
battery voltage returned to NUT is hard-coded to 24.0 V, which is annoying, but 
should not affect internal decisions about shutdown. Example: 
https://networkupstools.org/ddl/Cyber_Power_Systems/CP1500PFCLCD.html and 
https://github.com/networkupstools/nut/issues/459#issuecomment-325163688