On Thu, 6 Aug 2020, Todd Benivegna wrote:
... I grep’d the syslog and here’s the results:
Could you also grep for upsd and upsmon in the NAS log? Is this possible?
proton@proton:~$ sudo grep upsmon /var/log/syslog
Aug 6 19:19:09 proton upsmon[1552]: UPS ups@192.168.1.70 on battery
Aug 6 19:19:14 proton upsmon[1552]: UPS ups@192.168.1.70 on line power
Aug 6 19:19:44 proton upsmon[1552]: UPS ups@192.168.1.70: forced
shutdown in progress
Aug 6 19:19:44 proton upsmon[1552]: Executing automatic power-fail
shutdown
So proton is a slave, and is being made to shut down.
Aug 6 19:19:45 proton upsmon[1552]: Auto logout and shutdown proceeding
Aug 6 19:19:50 proton upsmon.conf: UPS status is
The variable USPstatus set by getUPSstatus was not in the environment for the
echo command. To get this to work, you'll have to put the upsc commands
directly in SHUTDOWNCMD, or create a short script and call the script in
SHUTDOWNCMD.
Aug 6 19:19:59 proton upsmon[1545]: UPS: ups@192.168.1.70 (slave) (power
value 1)
Could you tell us your topology? Which system is master and which is slave?
Do you have multiple slaves? The decision to shutdown is taken by the master,
not the slave.
Is it possible to run script http://rogerprice.org/NUT/nut-report on the NAS?
Could you run the script on one of the slaves and post the result here?
Roger
_______________________________________________
Nut-upsuser mailing list
Nut-upsuser@alioth-lists.debian.net
https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser