On Jan 25, 2022, at 2:51 PM, William Cole via Nut-upsuser 
<nut-upsuser@alioth-lists.debian.net> wrote:
> 
> I hope that this is an appropriate post for this group.  Please let me know 
> if it should go elsewhere.

Yes, this is a good place to ask general questions. However, you may want to 
subscribe to the list, at least temporarily, so that we do not need to manually 
approve your messages:

https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser

As such, you may have missed Roger's reply which looks like it went only to the 
list: 
https://alioth-lists.debian.net/pipermail/nut-upsuser/2022-January/012666.html

> I am running NUT on RaspberryPi 3B+ [RPi] units using Buster.  The NUT 
> version is 2.7.4.

Thanks for the info.
> 
> I have two UPS's in two different physical locations.  Each is attached to 
> its own RPi.
> Both UPS's are APCs but of different models.
> 
> I have one APC attached to an RPi w/NUT configured as a server with the 
> following script entries:
> ---------------------------------
> nut.conf
> MODE=netserver
> 
> ups.conf
> [APCES850Server]
>      driver=usbhid-ups
>      port=auto
>      desc=”APC ES850”
>      serial=4B2037P49872
>      pollinterval=15
>      vendorid=051d
> [APCES750Client]
>      driver=usbhid-ups
>      port=auto
>      desc=”APC ES750”
>      serial=3B0907X16989
>      pollinterval=15
>      vendorid=051d

It looks like you have the syntax correct for ups.conf, but the USB details 
like the serial number and vendorid should go in the ups.conf on the Pi that is 
directly connected to that UPS.

You can think of the client/server setup as follows: the server is providing 
the UPS status over the network to the clients, much as a simple file server 
has a local disk, and the files on that disk are available to other clients of 
that server.

> 
> upsmon.conf
> MONITOR APCES850Server@192.168.1.100 1 upsmon LASTPASS master
> MONITOR APCES750Client@192.168.1.101 1 upsremote LASTPASS slave
> 
> Usual entries for upsd.conf and upsd.users.
> -------------------------------
> The other APC is attached to a different RPi w/NUT configured as a client 
> with the following script entries:
> -------------------------------
> nut.conf
> MODE=netclient
> 
> ups.conf
> [no entries]
> 
> upsmon.conf
> MONITOR APCES850Server@192.168.1.100 1 upsmon LASTPASS master
> MONITOR APCES750Client@192.168.1.101 1 upsremote LASTPASS slave
> ------------------------------
> The server works fine.  The client will not connect, throwing a "UPS 
> APCES750Client@192.168.1.101 is unavailable"error.

If you look at the service status on 192.168.1.100, you will probably see that 
upsd was not able to connect to the ES750 over USB on that Pi. Since there is 
no entry for the ES750 in ups.conf on 192.168.1.101, that is why you get the 
"UPS ... is unavailable" error.

$ systemctl status nut-server
● nut-server.service - Network UPS Tools - power devices information server
   Loaded: loaded (/lib/systemd/system/nut-server.service; enabled; vendor 
preset: enabled)
   Active: active (running) since Fri 2022-01-14 21:07:31 EST; 1 weeks 4 days 
ago
 Main PID: 2187 (upsd)
...
Jan 14 21:07:31 <hostname> upsd[2023]: Connected to UPS [apc]: usbhid-ups-apc

The part that Roger and I aren't sure of is how you intend the rest of the 
monitoring to work.

Should the second Pi shut down when the UPS on the first Pi is exhausted? Or do 
you just want to log the status remotely?

As far as terminology, we covered the server/client side of things. There is 
also a similar concept of master/slave (exact terms to be changed later) which 
is more about which upsmon server (the master) waits for other clients (the 
slaves) to shut down before it does. It's more like a captain on a ship waiting 
for everyone else to get on the life rafts safely (or the captain goes down 
with the ship). If you do not want to create extra dependencies between the two 
Pis, each can have a "master" entry in its upsmon.conf that points to the 
directly-connected UPS.

-- 
Charles Lepple
clepple@gmail
_______________________________________________
Nut-upsuser mailing list
Nut-upsuser@alioth-lists.debian.net
https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser

Reply via email to