>From that I see you're better off using megatec than masterguard. I'll try to fix the battery charge bug tonight. I'll notify you when it has been commited to the SVN repository.
On 3/29/06, Mathias Mayrhofer <[EMAIL PROTECTED]> wrote: > I'm sure, it has two batteries! > > output as follows: > > startup: > ====== > > Network UPS Tools - UPS driver controller 2.1.0 > Network UPS Tools - MASTERGUARD UPS driver 0.23 (2.1.0) > > Found Q1 > > WH says <WH> with length 2 > New WH String found. Please report to maintainer > : Success > Found Q1 > WH says <WH> with length 2 > New WH String found. Please report to maintainer > : Success > MASTERGUARD UPS found > update info > Q1 Buffer is : 225.8 225.8 225.8 016 49.9 26.0 25.0 00001001 > value=225.8 > value=225.8 > value=225.8 > value=016 > value=49.9 > value=26.0 > value=25.0 > value=00001001 > Status is OL > > upsc: > ==== > > battery.voltage: 26.0 > driver.name: masterguard > driver.parameter.port: /dev/ttyS0 > driver.version: 2.1.0 > driver.version.internal: 0.23 > input.frequency: 49.9 > input.voltage: 225.8 > output.voltage: 225.8 > ups.load: 016 > ups.mfr: MASTERGUARD > ups.model: unknown > ups.status: OL > ups.temperature: 25.0 > > -- Carlos Rodrigues _______________________________________________ Nut-upsuser mailing list Nut-upsuser@lists.alioth.debian.org http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser