ons 2007-04-04 klockan 16:23 +1200 skrev Douglas Pearless: > Hi, > Hi Douglas, > I have a Comapq T2400H model 242688-003 and do not have the special > cable to connect it to my serial port. > > I have tried all sorts of cable wirings that I found on the net, > including ones for the powerware 5119 which appears to be the same > model. >
OK, I think you have seen this :-) ----------------------------------------------------- Part# 295245-003 (PowerRite Pro) Software: FailSafe-III UPS DB-9M DB-9F RS-232 Receive 1 <---------------------------< 3 TxD Transmit 2 <---------------------------< 2 RxD Common 4 <---------------------------< 5 SG PnP_En 6 <---------------------------< 7 RTS +----< 4 DTR +----< 6 DSR ------------------------------------------------------ And this should be the cable. And it is for smart mode, so you can not use it with the generic driver. > I have read the documentation that comes with NUT, tried to read the > source code and looked at the genericups code too. I have hit a bit > of a wall, does anyone have the pinout for a working cable for this > unit that works in the dumb or smart mode, and the ups.conf they > used?? This type of ups is talking upscodeII, so you need to test the upscode2 driver. If it acts like a T1500h you may need to add 'use_pre lf' into the 'ups.conf'. ups.conf should look something like this. [compaq] driver = upscode2 port = /dev/ttyS0 desc = "Compaq T2400h" manufacturer = "Compaq" input_timeout = 5 use_pre_lf = yes Regards Kjell P.S. Send you a pdf of list. _______________________________________________ Nut-upsuser mailing list Nut-upsuser@lists.alioth.debian.org http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser