Kjell Claesson wrote: >> The previous values were under load, which I forgot to mention. It has a >> ~500W server and 10W switch on it. >> > > Then the ups.load is low also. > But you should not do the LB shutdown test with the server attached. > It may power off without a warning.
The readings just before the nut initiated server shutdown due to LB was: % upsc xtreme battery.charge: 47.9 driver.name: powercom driver.parameter.linevoltage: 120 driver.parameter.manufacturer: XPCC driver.parameter.modelname: XVRT-1000 driver.parameter.pollinterval: 2 driver.parameter.port: /dev/ttyS0 driver.parameter.type: KIN1500AP driver.version: 2.2.2 driver.version.internal: $ Revision: 0.5 $ input.frequency: 0.00 input.voltage: 0.0 input.voltage.nominal: 120 output.frequency: 59.53 output.voltage: 13.3 ups.load: 85.5 ups.mfr: XPCC ups.model: XVRT-1000 ups.model.type: KIN1500AP ups.serial: Unknown ups.status: FSD OB LB BOOST The battery.charge dropped in increments of 5.0. It started at: % upsc xtreme battery.charge: 146.9 driver.name: powercom driver.parameter.linevoltage: 120 driver.parameter.manufacturer: XPCC driver.parameter.modelname: XVRT-1000 driver.parameter.pollinterval: 2 driver.parameter.port: /dev/ttyS0 driver.parameter.type: KIN1500AP driver.version: 2.2.2 driver.version.internal: $ Revision: 0.5 $ input.frequency: 0.00 input.voltage: 0.0 input.voltage.nominal: 120 output.frequency: 59.53 output.voltage: 14.1 ups.load: 67.1 ups.mfr: XPCC ups.model: XVRT-1000 ups.model.type: KIN1500AP ups.serial: Unknown ups.status: OB _______________________________________________ Nut-upsuser mailing list Nut-upsuser@lists.alioth.debian.org http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser