Citeren Mike Barber <badpa...@googlemail.com>:
Installed 2.4.1 using apt and installed in place of initial version
Found various web documents detailing that blazer_usb would probably be the
driver to use.
using usb.conf :
[UPS]
driver = blazer_usb
port = auto
and running the driver in debug mode gives the following :
[...]
Checking device (0001/0000) (001/003)
- VendorID: 0001
- ProductID: 0000
- Manufacturer: ATCL FOR UPS
- Product: ATCL FOR UPS
- Serial Number: ATCL FOR UPS
The VendorID / ProductID combination is bogus. The manufacturer of the
UPS was too cheap to apply for a real USB ID and made one up. This
means that this will give us no clue how to communicate with this
device based on this information. A few years ago we ran into this
combination for the first time and at that time we found out how to
talk to that particular device. However, this doesn't mean that yours
will work in the same way (it may be something completely different,
there is no way to tell).
There is a very small chance that one of the other subdrivers in
blazer_usb is able to talk to device. You'll have to help finding it
by specifying 'vendorid', 'productid' and 'subdriver' in ups.conf. See
'man 8 blazer' for more information. If this also fails to detect your
UPS you're basically out of luck. Unless *you* can provide us with the
protocol this device uses (ask the vendor, manufacturer, reverse
engineer it, whatever), we can't support it in NUT.
using Blazer_usb on 2.6 gives virtually the same output as 2.4.1
You'll definitely need to use this one for the above to have any
chance of success. Good luck.
Best regards, Arjen
--
Please keep list traffic on the list (off-list replies will be rejected)
_______________________________________________
Nut-upsuser mailing list
Nut-upsuser@lists.alioth.debian.org