Hello, I have a Best Ferrups 3.1KVA and I noticed that the percent battery voltage reported from upsc never gets above 69.9%. I believe there is a mistake in the driver. The battery percentage is calculated based on the High Battery Alarm Setpoint (59.6V) instead of the Ideal Voltage which is about 54V (4 batteries x 13.6V). I examined the source code and found that the variable fc.fullvolts is the result of querying parameter 67 from the UPS. This parameter is defined per Ferrups Tip 503 as: "The battery voltage at which the UPS sound a High Battery alarm" A better value to use in determining the percent battery voltage would be fc.idealbvolts which is calculated in the driver source...
I propose the following patch to fix the battery.charge (% battery full) reading. --- bestfcom.c.orig 2012-07-31 12:38:59.000000000 -0500 +++ bestfcom.c 2013-05-11 09:39:52.155279710 -0500 @@ -332,7 +332,7 @@ /* Compute battery percent left based on battery voltages. */ battpercent = ((vbatt - fc.emptyvolts) - / (fc.fullvolts - fc.emptyvolts) * 100.0); + / (fc.idealbvolts - fc.emptyvolts) * 100.0); if (battpercent < 0.0) battpercent = 0.0; else if (battpercent > 100.0) The patch is based on version 2.6.5 Thanks for your consideration. I know this is an old UPS (1995) but it still works and I'd like to keep using it :) -- Bo Kersey VirCIO - managed network solutions If it is free, you are the product. _______________________________________________ Nut-upsuser mailing list Nut-upsuser@lists.alioth.debian.org http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser