On Jun 2, 2014, at 12:25 PM, Andreas Lausch / TBT wrote: > > Hi, > > thanks for the reply. > > On 2014-05-29 05:21, Charles Lepple wrote: >>> Now my questions: >>> 1. should the blazer_ser's high voltage be the voltage during charging >>> or right after I've unplugged it from the mains? >> sounds like during charging (or more accurately, during float charging at >> the end of the cycle): >> >> http://www.networkupstools.org/docs/man/blazer.html#_extra_arguments > > Are you sure? If I put the 27.4 (reported voltage @ 100%) in the config, > battery.charge drops immediately when unplugged, because the reported > battery.voltage then is only 26.xV. (But I'm not sure the battery was at > 100% when I saw the 26.xV)
I'm pretty sure I wouldn't rely on a charge percentage derived this way ;-) As mentioned in the other thread about the tripplite_usb driver, apart from having two sets of calibration constants, one for OL and one for OB, there is no good way to have a one-size-fits-all calibration. My answer was based on the documentation, but you could make a case for the on-battery voltage. >>> 2. should the blazer_ser's low voltage be 21.6V (Low) or 19.2V (Shutdown)? >> From the calculations, I would guess 19.2V. In general, the LB signal comes >> when the battery is around 30%, so that there is still some charge left >> while the load is powering down. > > Yeah, I think so too. Either way, the UPS is making the LB determination, so if I had to rely on the low end of the charge scale, I'd test it. > >>> 3. Is there any way I can submit the high/low values, so they get >>> integrated into the driver or doesn't blazer_ser support voltage presets >>> per model? >> >> It doesn't look like it. >> >> Also, the blazer* drivers are no longer maintained, and are being replaced >> by the nutdrv_qx driver (which uses very similar code for these >> calculations, but the model-specific code is organized differently). > >> >> A comment in qx_initbattery() implies that some UPSes can provide the >> battery voltage range. You might try that driver (available in 2.7.1 and >> later) to see if it does this automatically. If not, you can check with the >> driver author to see about integrating some per-model defaults. >> > > Afaik blazer_* supports the same feature, but the power walker usvs don't > seem to report anything. > > I'm using NUT 2.6.3 from the Ubuntu 12.04.4 LTS repo and I have to stick to > that until 14.04.1 LTS comes out (July 24th) :/ > Anyway, looking at the subdrivers nutdrv_qx_*.c, I see neither a > "battery.voltage.high" nor the idea to make model-specific > assumptions/presets (only brand-specific (protocols)). We should probably look into ways to make it easier to build custom .deb files for Ubuntu. -- Charles Lepple clepple@gmail _______________________________________________ Nut-upsuser mailing list Nut-upsuser@lists.alioth.debian.org http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser