On Sun, 5 Feb 2017, Tim Richards wrote:

Setup: Active/Passive Two Node Cluster. Two UPSes (APC Smart-UPS 1500 C) with USB communication cables cross connected (ie UPS-webserver1 monitored by webserver2, and vice versa) to allow for stonith/fencing

OS OpenSuse Leap 42.2
NUT version 2.7.1-2.41-x86_64
Fencing agent: external/nut

Problem: When power fails to a single UPS, both nodes are shutdown. The node with the still powered UPS comes back up, but requires manual intervention to keep it providing services. I would like only the node with the “On Battery” UPS to shutdown.

I think your title hints at the solution. What is the advantage of the cross-connection of the UPS units? Wouldn't it be simpler to have each node connected to the UPS which supplies the power? This is easier to set up, extends easily to n servers, and is independent of the stonith/fencing which I assume you use for other purposes.

The resupply of services problem seems to be that NUT on the node that comes back up will not restart until the other node restarts.

With a simpler setup, this problem should go away.