Re: [Nut-upsuser] Synology NAS is shutting down Ubuntu servers after very brief power outage (fwd)
On Sun, 9 Aug 2020, Todd Benivegna wrote: upssched.conf (on Synology): CMDSCRIPT /usr/syno/bin/synoups upssched-cmd (on Synology): I don’t see this file. The CMDSCRIPT declaration says that in a Synology box the file that NUT calls upssched-cmd is called /usr/syno/bin/synoups. Could we see this file? Thanks. What is "Safe mode"? Is it complete power down?, or some sort of hibernation? If it's not a complete power down, how is the hibernation powered? "When the Synology NAS enters Safe Mode, it stops all services and unmounts volumes in order to prevent data loss and shut down (halt for EDS14) safely when the UPS device runs out of power. By default, the system enters Safe Mode when the UPS device starts running low on power. You can also specify the amount of time before the Synology NAS enters Safe Mode when power failure occurs. However, if the UPS device reaches low battery before the specified time, the system enters Safe Mode immediately. In situations where the Synology NAS shuts down during Safe Mode, it will automatically turn on when power is restored if you have enabled the Restart automatically after a power failure option (located at Control Panel > Hardware & Power > General)." This reads like typical sales literature. I admit to being none the wiser even after reading it several times. I gather this puts it in a state where it is ready for imminent power loss and won’t damage or lose any data. How long can this last? Who supplies the power to the NAS during "Safe mode"? Ok, I will comment that back out. That won’t interfere with anything? What user would it run as? Will it have access to upsmon.conf? Ubuntu very probably has user nut set up to run NUT and has the permissions set accordingly. If it's possible to execute "command ps -elf | grep nut" in a running NAS you will see user nut in action. Roger___ Nut-upsuser mailing list Nut-upsuser@alioth-lists.debian.net https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser
Re: [Nut-upsuser] Synology NAS is shutting down Ubuntu servers after very brief power outage (fwd)
On Aug 9, 2020, at 3:18 PM, Todd Benivegna wrote: > > Now they will spin-up on their own, but it takes 5-10 seconds. My thought > was if they can’t communicate initially, they assume the server is dead and > shut down. Would that make sense at all? Sorry to jump in the middle here, but this can occur in certain cases, when upsmon sees a server go dead *after seeing it go on battery*. See "DEADTIME" description: https://networkupstools.org/docs/man/upsmon.conf.html (defaults to 15 seconds) ___ Nut-upsuser mailing list Nut-upsuser@alioth-lists.debian.net https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser
Re: [Nut-upsuser] Synology NAS is shutting down Ubuntu servers after very brief power outage (fwd)
> Since it's NUT in the NAS which is deciding to order the shutdown, it would be > useful to see upsmon.conf, upssched.conf and upssched-cmd (or whatever > Synology > use if anything) from the NAS to see what criteria they use. upsmon.conf (on Synology): RUN_AS_USER root MONITOR ups@localhost 1 monuser secret master MINSUPPLIES 1 SHUTDOWNCMD "" NOTIFYCMD /usr/sbin/upssched POLLFREQ 5 POLLFREQALERT 5 HOSTSYNC 15 DEADTIME 15 POWERDOWNFLAG /etc/killpower NOTIFYFLAG ONLINE EXEC NOTIFYFLAG ONBATT EXEC NOTIFYFLAG LOWBATT EXEC NOTIFYFLAG NOCOMM EXEC NOTIFYFLAG COMMBAD IGNORE NOTIFYFLAG COMMOK IGNORE NOTIFYFLAG SHUTDOWN IGNORE NOTIFYFLAG FSD EXEC NOTIFYFLAG NOPARENT SYSLOG RBWARNTIME 43200 NOCOMMWARNTIME 300 FINALDELAY 5 upssched.conf (on Synology): CMDSCRIPT /usr/syno/bin/synoups PIPEFN /var/run/upssched.pipe LOCKFN /var/run/upssched.lock AT ONLINE * EXECUTE online AT ONLINE * CANCEL-TIMER fsd AT LOWBATT * EXECUTE lowbatt AT NOCOMM * EXECUTE nocomm AT FSD * EXECUTE fsd AT ONBATT * EXECUTE onbatt upssched-cmd (on Synology): I don’t see this file. Here are all the files in the ups folder: nutscan-usb.h ups.conf upsd.conf upsd.users upsmon.conf upssched.conf > What is "Safe mode"? Is it complete power down?, or some sort of hibernation? > If it's not a complete power down, how is the hibernation powered? "When the Synology NAS enters Safe Mode, it stops all services and unmounts volumes in order to prevent data loss and shut down (halt for EDS14) safely when the UPS device runs out of power. By default, the system enters Safe Mode when the UPS device starts running low on power. You can also specify the amount of time before the Synology NAS enters Safe Mode when power failure occurs. However, if the UPS device reaches low battery before the specified time, the system enters Safe Mode immediately. In situations where the Synology NAS shuts down during Safe Mode, it will automatically turn on when power is restored if you have enabled the Restart automatically after a power failure option (located at Control Panel > Hardware & Power > General)." I gather this puts it in a state where it is ready for imminent power loss and won’t damage or lose any data. I have enabled “Shutdown UPS when the system enter Safe Mode” and I have also enabled “Restart automatically after a power failure” as noted above. I have always had these two options enabled. Yesterday I recently disabled HDD Advanced Hibernation option as I thought that may interfere with NUT on my servers being able to communicate with the NUT server on the NAS, hence the immediate shutdown. Now they will spin-up on their own, but it takes 5-10 seconds. My thought was if they can’t communicate initially, they assume the server is dead and shut down. Would that make sense at all? HDD Hibernation essentially spins down the hard drives when there has been no activity. I had it set at one hour; I have since disabled that setting. I have not ever set the Synology itself to go to sleep or to auto-shutdown. From the Synology support site: You can specify the period of time hard disks remain idle before entering HDD hibernation mode. During HDD hibernation, hard disks stop spinning, reducing power consumption and extending the lifespan of hard disks. You can specify different periods of time for internal hard disks and external eSATA/USB hard disks. Phase 1: HDDs power down after a period of inactivity (idle time). You may go to DSM > Control Panel > Hardware & Power > HDD Hibernation to configure the length of inactivity for the HDDs to enter hibernation. Phase 2: Advanced Hibernation/Deep Sleep will be implemented for the HDDs to further reduce power consumption. You may go to DSM > Control Panel > Hardware & Power > HDD Hibernation to enable advanced HDD hibernation. > You should remove line 1 : RUN_AS_USER nut Ok, I will comment that back out. That won’t interfere with anything? What user would it run as? Will it have access to upsmon.conf? Thanks, Todd -- Todd Benivegna // t...@benivegna.com On Aug 9, 2020, 3:07 AM -0400, Roger Price , wrote: > On Fri, 7 Aug 2020, Todd Benivegna wrote: > > Hello Todd, sorry for the delay replying, I was away for a while. It's ok to > post configuration files in this list if blank lines and comments are removed. > > > On the Synology (I didn’t edit any of these files): > > ups.conf: https://hastebin.com/dedereqizi.shell > > pollinterval = 5 > [ups] > driver = usbhid-ups > port = auto > > > upsd.conf: https://hastebin.com/pupeseweda.css > > LISTEN 192.168.1.70 > LISTEN 2601:cf:8200:43d0:211:32ff:fe63:60d7 > LISTEN fe80::211:32ff:fe63:60d7 > LISTEN 127.0.0.1 > LISTEN ::1 > > > upsd.users: https://hastebin.com/ocenamecex.cs > > [monuser] > password = secret > upsmon master > > Since it's NUT in the NAS which is deciding to order the shutdown, it would be > useful to see upsmon.conf, upssched.conf and upssched-cmd (or whatever >
Re: [Nut-upsuser] Synology NAS is shutting down Ubuntu servers after very brief power outage (fwd)
On Sat, 8 Aug 2020, Todd Benivegna wrote: I just ran a manual test, killing power and see what happens. I set the Synology “Time before DiskStation goes into Safe mode” What is "Safe mode"? Is it complete power down?, or some sort of hibernation? If it's not a complete power down, how is the hibernation powered? to 5 minutes so I didn’t have to wait like an hour until it powered down. Here is the log: https://hastebin.com/ovuwilufeb.sql Aug 8 14:31:01 proton upsmon[1561]: UPS ups@192.168.1.70 on battery Aug 8 14:36:01 proton upsmon[1561]: UPS ups@192.168.1.70: forced shutdown in progress Aug 8 14:36:01 proton upsmon[1561]: Executing automatic power-fail shutdown Aug 8 14:36:01 proton upsmon[1561]: Auto logout and shutdown proceeding Aug 8 14:36:06 proton upsmon.conf: UPS status [FSD OB DISCHRG]:85 Notice the effect of the upsmon FINALDELAY 5 declaration in the last line. Status [FSD OB DISCHRG] is what one would expect in a slave. I see the UPS has lost 15% of it's charge in 5 minutes. Everything appeared to be normal; the servers powered off and the Synology went into safe mode. Power was then cut to the Synology and my UPS turned off. I assume power was cut to the Synology because the UPS disconnected it's power outlets (often referred to as "UPS turns off"). Could it be something like the Synology drives were in hibernation and the Synology wasn’t responding (was probably coming out of hibernation - it takes maybe 5-10 seconds) and NUT thought the server was dead and shut everything down? On that note, I did have the Synology set to hibernate/spin down the disks after 1 hour, but just disabled that just in case; will be on all the time now. You think that was possibly the problem? It would be interesting to see what the Synology log says for hibernation, upsd and upsmon for a) a manual test, and b) a real wall power failure. Roger___ Nut-upsuser mailing list Nut-upsuser@alioth-lists.debian.net https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser
Re: [Nut-upsuser] Synology NAS is shutting down Ubuntu servers after very brief power outage (fwd)
On Sat, 8 Aug 2020, Todd Benivegna wrote: Updated upsmon.conf: https://hastebin.com/jisinaquso.pl You should remove line 1 : RUN_AS_USER nut Lines 12-21: it would be possible to display more information, such as the UPS status, but this requires pointing NOTIFYCMD to upssched and then using a upssched-cmd script to display details of each event. No, the Synology and the three servers are all on the one UPS (also my switch and spare monitor). All these are super low power devices (two Intel NUCs and a Raspberry Pi) so at idle the draw like 50-75w and at max load it’s like 100-150w tops. UPS is rated for 300w. In that case, nothing stops you from using one of the "p" Ubuntu machines as the master with the Synology NAS as a slave. See https://community.synology.com/enu/forum/1/post/119995 Roger___ Nut-upsuser mailing list Nut-upsuser@alioth-lists.debian.net https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser
Re: [Nut-upsuser] Synology NAS is shutting down Ubuntu servers after very brief power outage (fwd)
On Fri, 7 Aug 2020, Todd Benivegna wrote: I don’t think I am able to run that script. If you can, I wouldn’t know how. You have to activate SSH on the NAS, log in to the NAS as root (admin) and create a temporary directory. Based on what I read on a french language site, the commands are: mkdir /volume1/tmp cd /volume1/tmp You can then install the script and run it: wget http://rogerprice.org/NUT/nut-report ./nut-report Roger___ Nut-upsuser mailing list Nut-upsuser@alioth-lists.debian.net https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser
Re: [Nut-upsuser] Synology NAS is shutting down Ubuntu servers after very brief power outage (fwd)
On Fri, 7 Aug 2020, Todd Benivegna wrote: Hello Todd, sorry for the delay replying, I was away for a while. It's ok to post configuration files in this list if blank lines and comments are removed. On the Synology (I didn’t edit any of these files): ups.conf: https://hastebin.com/dedereqizi.shell pollinterval = 5 [ups] driver = usbhid-ups port = auto upsd.conf: https://hastebin.com/pupeseweda.css LISTEN 192.168.1.70 LISTEN 2601:cf:8200:43d0:211:32ff:fe63:60d7 LISTEN fe80::211:32ff:fe63:60d7 LISTEN 127.0.0.1 LISTEN ::1 upsd.users: https://hastebin.com/ocenamecex.cs [monuser] password = secret upsmon master Since it's NUT in the NAS which is deciding to order the shutdown, it would be useful to see upsmon.conf, upssched.conf and upssched-cmd (or whatever Synology use if anything) from the NAS to see what criteria they use. Roger___ Nut-upsuser mailing list Nut-upsuser@alioth-lists.debian.net https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser