Re: [Nut-upsuser] Info on Cyber Power CP1500AVRLCDa

2022-06-06 Thread Phil Chadwick
stefa...@karandreas.gr wrote:

> Can you share a link to where the manual describes ups.delay.start? I 
> found
> some information but not the complete description you mention here.
> For ondelay=0 what happens? The load instantly returns on UPS shutdown
> or the bug doesn't trigger?

Hi Stefanos,

For "ondelay=0", the load returns immediately the wall power returns.

I should mention for clarity that "ups.delay.start" is set, by nut at
startup, from the value of "ondelay" in ups.conf.

However, I'm in the embarrassing situation of having to retract what I
said about "ups.delay.start".

Your question prompted me to verify my assertions, and I found this:

https://networkupstools.org/docs/man/usbhid-ups.html

which says of ondelay:

"Set the timer for the UPS to switch on in case the power returns
after the kill power command had been sent, but before the actual
switch off.  This ensures the machines connected to the UPS are,
in all cases, rebooted after a power failure.

"The default value is 30 (in seconds).  Usually this must be greater
than offdelay, but the driver will not warn you upon startup if it
isn't.  Some UPSes will restart no matter what, even if the power is
(still) out at the moment this timer elapses.  In that case, you could
see whether setting ondelay = -1 in ups.conf helps.

"Note that many CPS models tend to divide this delay by 60 and round
down, so the minimum advisable value is 120 to allow a short delay
between when the UPS shuts down, and when the power returns."

So my interpretation of "ups.delay.start" (as being applied after the
return of wall power) was coloured by a lot of research that all turned
out to be wrong.  In my defense, I was led astray by many others who
have trod the same path.  Sorry...

My next step will be to set offdelay=90, ondelay=120, and see how the
UPS behaves.
 
I still don't have any clear idea of how to delay restarting the load
while the batteries re-charge after an outage, so shutting down on a
"battery low" condition (and avoiding an infinite shutdown loop) remains
a challenge.

Cheers,


-- 
Phil

Blessed are the young, for they shall inherit the national debt.
-- Herbert Hoover

___
Nut-upsuser mailing list
Nut-upsuser@alioth-lists.debian.net
https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser


Re: [Nut-upsuser] Info on Cyber Power CP1500AVRLCDa

2022-06-06 Thread stefanos

On 2022-06-05 09:06, Phil Chadwick wrote:


Hi,

I have a CyberPower CP1500EPFCLCD.

I live in a rural location and experience frequent power failures.

I run a nut server on a FreeBSD host named "sherman".  It has a USB
connection to the CP1500EPFCLCD, using the usbhid-ups driver.  I don't 
use
nut clients, preferring to use one-shot root privileged ssh keys to 
execute
remote commands (i.e. shutdown) on the "network peers" of the nut 
server.


The CP1500EPFCLCD has firmware "issues", and I expect that there's a 
very

good chance that the CP1300EPFCLCD is the same.

The USB connection experiences a transient disconnect when power drops.


If the connection loss lasts couple sec max I guess it's something I and 
NUT
can live with, since as you mention it doesn't seem to affect how NUT 
operates.
I received another reply from the list that mentioned that for the 900VA 
model
there was no problem with the USB connection. I have to wonder whether 
that is

a result of the ephemeral connection loss.

The major firmware issue I tripped over is with "ups.delay.start".  
See:


  
https://alioth-lists.debian.net/pipermail/nut-upsuser/2018-October/011253.html


The nut manual says set ups.delay.start (default 30) as the interval to 
wait

before restarting the load (seconds) [AFTER UPS power returns].  The
CyberPower CP1500EPFCLCD UPS restarts ups.delay.start seconds after the 
UPS
is shutdown REGARDLESS of the wall power status.  i.e. regardless of 
mains

status:

  - ondelay=0,  UPS powers on the load when mains return
  - ondelay=-1, UPS never powers on the load, even when mains return
  - ondelay=xx, UPS powers on the load after xx (roughly) seconds
after UPS shutdown is executed.

I have reported this issues to CyberPower support, but got no 
satisfactory

resolution.  It's a serious problem...

This bug makes using "battery.charge.low" pretty much impossible, 
because

with a low battery you need to re-charge the battery AFTER wall power
returns and BEFORE restarting the load to power up the clients -- lest
you go into an infinite shutdown/reboot loop.  The faulty handling of
ups.delay.start prevents the battery from re-charging to a workable 
level

after discharge (unless you set ondelay=-1, which means you can't power
up automatically).

Can you share a link to where the manual describes ups.delay.start? I 
found

some information but not the complete description you mention here.
For ondelay=0 what happens? The load instantly returns on UPS shutdown 
or

the bug doesn't trigger?

Thanks,
Stefanos

___
Nut-upsuser mailing list
Nut-upsuser@alioth-lists.debian.net
https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser


Re: [Nut-upsuser] Info on Cyber Power CP1500AVRLCDa

2022-06-06 Thread Mike via Nut-upsuser
On 6/5/2022 7:16 AM, Charles Lepple via Nut-upsuser wrote:
> [snip]
>
> Updates to the DDL can be requested here:
> 
>https://github.com/networkupstools/nut-ddl/issues
>

I was not aware of that repository.

Thanks for the pointer...






___
Nut-upsuser mailing list
Nut-upsuser@alioth-lists.debian.net
https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser


Re: [Nut-upsuser] Info on Cyber Power CP1500AVRLCDa

2022-06-05 Thread Charles Lepple via Nut-upsuser
On Jun 5, 2022, at 5:54 AM, Greg Troxel wrote:
> 
> So having documentation per model that enables buying something that
> works seems key, and I don't find that.
[...]
> Sorry, I did find the compat list
> 
> https://networkupstools.org/stable-hcl.html
> 
> but I'm not really clear where the sort of extended discussion you are
> providing belongs.  (I am sure it's useful.)

Individual fields can be flagged with messages and links in the DDL:

   https://networkupstools.org/ddl/Cyber_Power_Systems/CP1000PFCLCD.html

   https://networkupstools.org/ddl/Cyber_Power_Systems/CP1500AVRLCDa.html

and if I understand Phil's post correctly, he is referring to this firmware 
issue regarding ups.delay.start:

   https://github.com/networkupstools/nut/issues/625

Updates to the DDL can be requested here:

   https://github.com/networkupstools/nut-ddl/issues

-- 
Charles Lepple
clepple@gmail



___
Nut-upsuser mailing list
Nut-upsuser@alioth-lists.debian.net
https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser


Re: [Nut-upsuser] Info on Cyber Power CP1500AVRLCDa

2022-06-05 Thread Greg Troxel

Sorry, I did find the compat list

https://networkupstools.org/stable-hcl.html

but I'm not really clear where the sort of extended discussion you are
providing belongs.  (I am sure it's useful.)


signature.asc
Description: PGP signature
___
Nut-upsuser mailing list
Nut-upsuser@alioth-lists.debian.net
https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser


Re: [Nut-upsuser] Info on Cyber Power CP1500AVRLCDa

2022-06-05 Thread Greg Troxel

Thanks for posting all those details; they are interesting.

I think it would be helpful to publish the config, at least the nut
logic part, and the details of cyberpower actual vs documented behavior.
(nut github wiki if Jim thinks that makes sense?)  Or maybe there is a
better place.

It seems that while how a UPS has to behave to reliably and safely
handle loss of power and restart, with all the possible sequencing, is
pretty well understood on this list, a lot of devices don't do it right.
So having documentation per model that enables buying something that
works seems key, and I don't find that.

Perhaps a warning not to buy cyberpower products would result in bug
fixes.  Perhaps not.


It strikes me that it should be possible to express start delay as e.g.

  wait until both are true:
power has been stable for 120s
battery is at least 80% charged



For your own situation, I wonder if this is a job for a microcontroller
and a bunch of relays, to patch up your UPS and make your power
sequencing do what you want.  Or a tiny computer like an RPI, maybe with
its own extended battery, or hooked into your dhcp server.  Maybe that's
a crazy idea, and I know it has a lot of downsides.



signature.asc
Description: PGP signature
___
Nut-upsuser mailing list
Nut-upsuser@alioth-lists.debian.net
https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser


Re: [Nut-upsuser] Info on Cyber Power CP1500AVRLCDa

2022-06-05 Thread Phil Chadwick
stefa...@karandreas.gr wrote:
> 
> Do you have by any chance the CyberPower CP1300EPFCLCD? I would 
> personally be interested
> in the variables it supports as I am thinking of buying that model to 
> replace an APC BX1400
> and I would like to know if it supports changing battery.charge.low etc.
> 
> I have also read 1-2 reviews for the specific model that mention that it 
> loses USB
> connectivity when switching to battery and back which would be 
> disastrous for NUT.
> Any feedback you have on that or the CyberPower model(s) would be most 
> helpful!

Hi,

I have a CyberPower CP1500EPFCLCD.

I live in a rural location and experience frequent power failures.

I run a nut server on a FreeBSD host named "sherman".  It has a USB
connection to the CP1500EPFCLCD, using the usbhid-ups driver.  I don't use
nut clients, preferring to use one-shot root privileged ssh keys to execute
remote commands (i.e. shutdown) on the "network peers" of the nut server.

The CP1500EPFCLCD has firmware "issues", and I expect that there's a very
good chance that the CP1300EPFCLCD is the same.

The USB connection experiences a transient disconnect when power drops.
Here is one of many identical examples from /var/log/messages.  However,
nut seems to handle the USB disconnects without problems:

May 23 04:01:31 sherman squid[31854]: Squid Parent: (squid-1) process 31856 
started
May 23 10:12:31 sherman kernel: ugen2.2:  at usbus2 
(disconnected)
May 23 10:12:32 sherman kernel: ugen2.2:  at usbus2
May 23 10:12:38 sherman nut-notify[33055]: UPS cp1500 onbatt
May 23 10:12:44 sherman nut-notify[33097]: UPS cp1500 
five-minute-warning-timer
May 23 10:16:43 sherman nut-notify[33141]: UPS cp1500 
one-minute-warning-timer
May 23 10:17:43 sherman nut-notify[33185]: UPS cp1500 shutdown-timer
May 23 10:17:43 sherman upsmon[1225]: Executing automatic power-fail 
shutdown
May 23 10:17:43 sherman upsmon[1225]: Auto logout and shutdown proceeding
May 23 10:17:44 sherman nut-shutdown[33227]: nut power-fail network 
shutdown sequence commencing
May 23 10:17:44 sherman nut-shutdownpeers[33237]: nut shutdown peers alert: 
shutting down strand
May 23 10:17:47 sherman nut-shutdownpeers[33249]: nut shutdown peers alert: 
shutting down fable
May 23 10:17:49 sherman nut-shutdownpeers[33259]: nut shutdown peers alert: 
shutting down mith
May 23 10:17:58 sherman nut-shutdownpeers[33269]: nut shutdown peers alert: 
shutting down orac
May 23 10:18:00 sherman nut-shutdownpeers[33279]: nut shutdown peers alert: 
shutting down pi3b
May 23 10:18:02 sherman nut-shutdownpeers[33289]: nut shutdown peers alert: 
skipping pi4 (not up)
May 23 10:18:03 sherman shutdown[33295]: power-down by root

The major firmware issue I tripped over is with "ups.delay.start".  See:

  https://alioth-lists.debian.net/pipermail/nut-upsuser/2018-October/011253.html

The nut manual says set ups.delay.start (default 30) as the interval to wait
before restarting the load (seconds) [AFTER UPS power returns].  The
CyberPower CP1500EPFCLCD UPS restarts ups.delay.start seconds after the UPS
is shutdown REGARDLESS of the wall power status.  i.e. regardless of mains
status:

  - ondelay=0,  UPS powers on the load when mains return
  - ondelay=-1, UPS never powers on the load, even when mains return
  - ondelay=xx, UPS powers on the load after xx (roughly) seconds
after UPS shutdown is executed.

I have reported this issues to CyberPower support, but got no satisfactory
resolution.  It's a serious problem...

This bug makes using "battery.charge.low" pretty much impossible, because
with a low battery you need to re-charge the battery AFTER wall power
returns and BEFORE restarting the load to power up the clients -- lest
you go into an infinite shutdown/reboot loop.  The faulty handling of 
ups.delay.start prevents the battery from re-charging to a workable level
after discharge (unless you set ondelay=-1, which means you can't power
up automatically).

To work around this problem, I run /usr/local/bin/nut-shutdown 5 minutes
after wall power drops.  It shuts down all the network peers using a
one-shot ssh key.  BIOS configurations allow everything to reboot when the
UPS supplies power immediately the wall power returns.  With my 300W load, 
the 5 minute delay ensures that the battery reserve is sufficient for a
restart, and avoids bouncing around any battery low condition.

I also regret not having an ability to delay load supply on each of the UPS
power outputs, and will look for that feature next time I buy a UPS.  The
fact is that I really need to bring up my network, firewall, and DHCP server
BEFORE the rest of the general computer systems, and the CP1500EPFCLCD can't
do that.  My small home network won't boot up properly unless the power is
sequenced to requirements (I really do need the DHCP server up first).  So I
find myself writing rc scripts to delay booting on some clients after a
power failure...


Re: [Nut-upsuser] Info on Cyber Power CP1500AVRLCDa

2022-06-04 Thread stefanos

On 2022-06-03 19:56, Mike via Nut-upsuser wrote:

The hardware page for this UPS has some info about what variables are
supported.

Here is some more info from my install.  Let me know if this type of
info is useful, as I can supply it for a couple other UPS's.

thanks!



Do you have by any chance the CyberPower CP1300EPFCLCD? I would 
personally be interested
in the variables it supports as I am thinking of buying that model to 
replace an APC BX1400

and I would like to know if it supports changing battery.charge.low etc.

I have also read 1-2 reviews for the specific model that mention that it 
loses USB
connectivity when switching to battery and back which would be 
disastrous for NUT.
Any feedback you have on that or the CyberPower model(s) would be most 
helpful!


Stefanos

___
Nut-upsuser mailing list
Nut-upsuser@alioth-lists.debian.net
https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser


[Nut-upsuser] Info on Cyber Power CP1500AVRLCDa

2022-06-03 Thread Mike via Nut-upsuser
The hardware page for this UPS has some info about what variables are
supported.

Here is some more info from my install.  Let me know if this type of
info is useful, as I can supply it for a couple other UPS's.

thanks!




OpenBSD 7.1 (amd64)
NUT 2.8.0

https://networkupstools.org/ddl/Cyber_Power_Systems/CP1500AVRLCD.html

# upsc ups2
battery.charge: 95
battery.charge.low: 10
battery.charge.warning: 20
battery.mfr.date: CPS
battery.runtime: 23887
battery.runtime.low: 300
battery.type: PbAcid
battery.voltage: 26.9
battery.voltage.nominal: 24
device.mfr: CPS
device.model: CP1500AVRLCDa
device.serial: [redacted]
device.type: ups
driver.flag.onlinedischarge: enabled
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.parameter.productid: 0501
driver.parameter.synchronous: auto
driver.parameter.vendorid: 0764
driver.version: 2.8.0
driver.version.data: CyberPower HID 0.6
driver.version.internal: 0.47
driver.version.usb: libusb-1.0.23 (API: 0x1000107)
input.voltage: 117.0
input.voltage.nominal: 120
output.voltage: 117.0
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.delay.start: 30
ups.load: 0
ups.mfr: CPS
ups.model: CP1500AVRLCDa
ups.productid: 0501
ups.realpower.nominal: 900
ups.serial: [redacted]
ups.status: OL CHRG
ups.test.result: No test initiated
ups.timer.shutdown: -60
ups.timer.start: -60
ups.vendorid: 0764


# upscmd -l ups2
Instant commands supported on UPS [ups2]:

beeper.disable - Disable the UPS beeper
beeper.enable - Enable the UPS beeper
beeper.mute - Temporarily mute the UPS beeper
beeper.off - Obsolete (use beeper.disable or beeper.mute)
beeper.on - Obsolete (use beeper.enable)
load.off - Turn off the load immediately
load.off.delay - Turn off the load with a delay (seconds)
load.on - Turn on the load immediately
load.on.delay - Turn on the load with a delay (seconds)
shutdown.return - Turn off the load and return when power is back
shutdown.stayoff - Turn off the load and remain off
shutdown.stop - Stop a shutdown in progress
test.battery.start.deep - Start a deep battery test
test.battery.start.quick - Start a quick battery test
test.battery.stop - Stop the battery test