On Nov 12, 2014, at 5:46 AM, Thiago Wiezbicki <thiago...@gmail.com> wrote:

> 
> 
> Device Manufacturer: NHS
> Device Name: Expert C Online 6000
> 
> upsc output:
> 
> battery.charge: 100
> battery.current: 0.6
> battery.date: 01012014
> battery.runtime: 00000
Quick question: does "battery.runtime" update when the device is on battery, or 
is this field always zero?
> battery.runtime.low: 59940
"battery.runtime.low" should be the number of seconds remaining before 
switching to "LB" status. This seems large, even for a 6000 VA UPS. Is this 
configurable?
> battery.temperature: 29
> battery.voltage: 210.5
210.5 V seems reasonable for the specifications. Is there a way in the SEC 
protocol to report "battery.voltage.nominal"?
> device.mfr: NHS Sistemas de Energia
> device.model: EXPERT GIII  8kVA
> device.type: ups
> driver.name: gamatronic
> driver.parameter.pollinterval: 20
> driver.parameter.port: /dev/ttyACM0
For the HCL, should we list this as a serial UPS, or is it USB that is 
auto-detected by the Linux kernel as a USB-to-serial converter?

If it is the latter, what are the USB VendorID and ProductID? You can send the 
output of "lsusb -v" if you prefer. (This will help others with non-Linux 
systems.)
> driver.version: 2.6.3
> driver.version.internal: 0.02
> input.frequency: 60.1
> input.transfer.high: 265
> input.transfer.low: 165
> input.voltage: 217.0
> input.voltage.nominal: 220
> output.current: 0.0
> output.frequency: 60.1
> output.voltage: 120.8
> ups.firmware: EXOL(02).21
> ups.id: ----------------
Does "ups.id" usually report a unique ID, or did you remove it? (No worries if 
you did; we will just mark it as such in the DDL).
> ups.load: 000
> ups.mfr: NHS Sistemas de Energia
> ups.model: EXPERT GIII  8kVA
> ups.power.nominal: 08000
> ups.status: OL
> 
> 
> I tested shutdown sequence when battery is low and computer turned off. 
> After, the UPS shuts down to and turn on when the energy came back. All it 
> looks ok.
Just to confirm, the shutdown occurred via upsmon recognizing "OB LB" status on 
the UPS?
> Link to the description:  http://www.nhs.com.br/produtos_interna/id/TWpFeQ==
> 
> 
> We're brazilian manufacturer of this device and used the SEC 2400 protocol 
> with full support. All it's working ok with gamatronic driver.

Thanks for the information! We appreciate vendor support for testing.

-- 