My understanding is that NUT provides a mechanism to shut down multiple systems protected by multiple UPS's in a given order. For example to shutdown the users before their NFS server.

1. man ups.conf says

sdorder Optional. When you have multiple UPSes on your system, you usually need to turn them off in a certain order. upsdrvctl shuts down all the 0s, then the 1s, 2s, and so on. To exclude a UPS from the shutdown sequence, set this to -1.

2. config-notes.txt gives an example

To set the order in which your UPSes receive the shutdown commands, define the 'sdorder' value in your ups.conf.

        [bigone]
                driver = usbhid-ups
                port = auto
                sdorder = 2

        [littleguy]
                driver = mge-shut
                port = /dev/ttyS0
                sdorder = 1

        [misc]
                driver = blazer_ser
                port = /dev/ttyS1
                sdorder = 0

The order runs from 0 to the highest number available. So, for this configuration, the order of shutdowns would be 'misc', 'littleguy', and then 'bigone'.

3. But in upsdrvctl.c I see

/* walk UPS table and send command to all UPSes according to sdorder */
static void send_all_drivers(void (*command)(const ups_t *))
{
        ups_t   *ups;
        int     i;

...
        for (i = 0; i <= maxsdorder; i++) {
                ups = upstable;
                while (ups) {
                        if (ups->sdorder == i)
                                command(ups);
                        ups = ups->next;
                }
        }
}

These nested loops will execute in a few milleseconds, effectively shutting down all the UPS units at the same time rather than in a paced sequence.

I see nothing that ensures that all the "0"s are effectively shut down before starting the shutdown of the "1"s.

Is there something in the sdorder logic that I am missing?