Citeren Philip Tait phi...@subaru.naoj.org:
Using 'mbrowse', I explored the MIB, and found that this particular
model (AP341/342) has everything under .1.3.6.1.4.1.476
(iso.org.dod.internet.private.enterprises.emerson), which, from looking
at the source for 2.4.1, seems to be not supported. I
Citeren Svein Skogen (Listmail Account) svein-listm...@stillbilde.net:
The relevant parts of my ups.conf is the following:
[1500LCD]
driver = usbhid-ups
vendorid=0764
productid=0501
vendor=CPS
port = /dev/ugen3.5
desc = My Cyberpower 1500 LCD
Citeren Daryl Sayers da...@ci.com.au:
I am running an older version of nut (2.0.2) on a FreeBSD 4.11 machine.
Please upgrade to a more recent version. The one you're using now is
well over five years old and is no longer supported.
[...]
1. Why are there so many failed - Data stale
Citeren Gene Heskett gene.hesk...@gmail.com:
Well, /etc/hal/fdi is now empty, and because I'd killed hald, I had to reboot
with the reset button, no keyboard or mouse, but the above condition remains,
and the nut driver is dead again for the same reason, it cannot take
possession of
Citeren Gene Heskett gene.hesk...@gmail.com:
There is also a missing /etc/sysconfig/ups file, which I have NDI what to put
into, so that bit of code in the init.d/ups is commented out, and
SERVER=master is set in it.
NUT doesn't use a /etc/sysconfig/ups file (this is probably added by
Citeren Kjell Claesson kjell.claes...@epost.tidanet.se:
Hi, do we have any active developer on the powercom driver.
As far as I know, no.
It seems to support the XPCC ups. The problem seems to be
the calculation of the voltage and ups.load.
OK, nothing essential. It would be nice to have
Citeren Marc Franquesa m...@l3jane.net:
My UPS is a Eaton Ellipse 1000S (But its identified as MGE Ellipse
0463:).
That's because part of the company MGE that originally acquired the
vendorid 0463 is now owned by Eaton. They still use the 'old' vendorid
for the .
I have been using
Citeren Arjen de Korte nut+us...@de-korte.org:
If you upgrade to nut-2.4.1, you could try adding the 'pollonly' flag
Sorry, this should have been the SVN trunk version. This is only
available in the development version.
to 'ups.conf' entry for this UPS. The problems seem to be related
Citeren Gene Heskett gene.hesk...@gmail.com:
You requested logs, which I sent, and which were not commented on in any
reply I received. Those logs show the usbhid-ups/belkin driver combination
losing comm with the ups and having to redo its search for the ups several
times a minute, but you
Citeren Roger Price ro...@rogerprice.org:
Hi, its only a minor wrinkle, but repeated %s in NOTIFYMSG seem to
be ignored.
Yes. This line is a simple 'printf' style formatting string in which
exactly one %s can be used. If you want more freedom in what is
printed, look under the NOTIFYCMD
Citeren Gene Heskett gene.hesk...@gmail.com:
No, you didn't read the INSTALL file. These are the build in defaults
if you don't tell configure where it should install things.
Ya mean its not the usual boilerplate? ;) IMO the defaults should at least
be sane.
The defaults are sane. It's
Citeren Gene Heskett gene.hesk...@gmail.com:
Something is confused here, and I don't think its all me. Where do I put
those miss-placed files so it stands a snowballs chance in that famous place
of working?
I honestly don't know. I don't use Fedora, so I don't have the
slightest clue where
Citeren Yury V. Zaytsev y...@shurup.com:
Please keep the list traffic on the list so that the others can benefit.
But please note that the messages are in English. If it is in Russian,
feel free to take it off-list.
Best regards, Arjen
--
Please keep list traffic on the list
Citeren Gene Heskett gene.hesk...@gmail.com:
Ping?
I didn't comment to that message (for exactly the reasons in the
subject field) and you seemed to be in the process of figuring stuff
out yourself (which we prefer, since then people actually learn,
instead of us developers telling them
Citeren Gene Heskett gene.hesk...@gmail.com:
2.4.1 now installed, using default ./configure
I had to make a bunch of directories move all the .conf files cuz the
config path seems scrambled, its /usr/local/ups/etc, s/b /usr/local/etc/ups
IMO. Bug?
No, you didn't read the INSTALL file. These
Citeren Gene Heskett gene.hesk...@gmail.com:
Just starting it with the fedora service command gets this:
[r...@coyote rules.d]# service ups start
/etc/sysconfig/ups: line 4: UPSD_OPTIONS: command not found
Starting UPS driver controller:[FAILED]
Starting upsd:
Citeren Yury V. Zaytsev y...@shurup.com:
[...]
It sends a power back e-mail no matter what, but probably we can live
with it.
This is trivial to script. Create an empty file somewhere your
CMDSCRIPT has write access to when the 'linedown' timer elapses (ie,
when you send the warning
Citeren Yury V. Zaytsev y...@shurup.com:
I know that for now I can rip the sources of some of the SRPMs floating
around etc. but I guess this is something that is ought to be fixed
ASAP.
The sources are also still available through
http://old.networkupstools.org/source.html
I agree
Citeren Ole Hoppe ole.ho...@gmail.com:
Of course they want you to purchase their PowerChute for Linux, so
this is of course not satisfactory. But maybe you can extract
another alternative to instruct the UPS for a shutdown/reboot?
As I already told in a previous message, we attempt several
Citeren Ole Hoppe ole.ho...@gmail.com:
Thank you so much for your prompt explanations. Had selected the UPS
merely by load requirements not knowing that such seemingly basic
functionality may not be supported by entry-level UPSs. We can live
with that.
Well, according to the info on the
Citeren Ole Hoppe ole.ho...@gmail.com:
What could be wrong that prevents UPS from turning itself on again?
The UPS might not support this, in which case there is nothing we can
do about this. The APC Back-UPS CS 350 is an entry level consumer
grade UPS which is intended to power small
Citeren Jelle de Jong jelledej...@powercraft.nl:
Could somebody help me with some configuration snippet to get this
working?
[apc1]
driver = usbhid-ups
port = auto
serial = 12345678
[apc2]
driver = usbhid-ups
port = auto
serial = 12345678
Your UPS devices must be
Citeren Jelle de Jong jelledej...@powercraft.nl:
As an flow up: I read the usbhid-ups man page, and I am using the
setup described in the attachment, it seems usbhid-ups is not
detecting the serial numbers. Any idea's?
This looks like a permissions problem. Try running the drivers as root
Citeren Arjen de Korte nut+us...@de-korte.org:
This is clear, the old UPS doesn't seem to use the input reports (at
least not very frequently), so the chances of collisions with
feature reports are less.
But looking at the data again, I also noticed that the new UPS doesn't
use them very
Citeren Thomas Gutzler thomas.gutz...@gmail.com:
The 'old' UPS might not be using interrupt reports and therefor, we
don't see collisions. Could you run it in debug mode (one minute will be
enough) to check if this is indeed the case?
The logfile is attached; one with each version.
This is
Citeren Thomas Gutzler thomas.gutz...@gmail.com:
In summary:
- no EMI (port re-connect) for the 'old' ups
- 68 and 76 USBDEVFS_CONTROL errors for the 'old' ups over the first and
second period
- 323 and 314 USBDEVFS_CONTROL errors for the 'new' ups over the first
and second period
The 'old'
Citeren Guillaume Vachon gvac...@infoglobe.ca:
I just got myself 2 APC Back-UPS CS 350
I downloaded the stable nut tar.gz installed it.
This is not the first time i install and configure nut so i used the
same configuration as on my other server as i always did. Then i made
the 2 required
Citeren Thomas Gutzler thomas.gutz...@gmail.com:
Ok, I've checked out svn://svn.debian.org/nut/trunk
(why does the website say it's version 2.5, when configure.in says
AC_INIT(nut, 2.4.1)?)
Probably because we forgot to update this in the trunk. We don't
really use this value for
Citeren Thomas Gutzler thomas.gutz...@gmail.com:
Are there any thoughts, comments or suggestions for this problem or
should I just ignore it?
There are some thoughts, but they are not much different from what you
may have already found in the archives.
I keep getting the following
Citeren Thomas Gutzler thomas.gutz...@gmail.com:
I have set pollfreq to 120; wasn't aware that there is an event based
messaging system in place next to the polling. I also tried changing
ups.test.interval (as suggested by Arnaud) but it didn't exist and the
only other interval variable I found
Citeren Arnaud Quette aquette@gmail.com:
for the system load, I still have to do a powertop pass and some more
tuning to improve the driver.
We might also want to spread out the full polls, so that they are not
sent one after the other. So instead of doing either a quick or full
poll,
Citeren JW Simpson j...@swajime.com:
I tried starting this with the PowerCom BNT-other driver ... and it
looks like it's all running, except I can now see ups.model:
KIN-2200AP. :-|
I'm guessing that I should set it up with the KIN driver then ???
I honestly don't know, you'll have to
Citeren Jesper Klit Jensen jes...@jensen-net.org:
Can somebody guide me to what I do wrong or how I can find the
issue. The port is /dev/ttyS1 that is where Cyberpowers own software
connect.
Try running the powerpanel driver with debugging enabled:
/path/to/powerpanel -DDD -a uspname
Citeren Charles Lepple clep...@gmail.com:
If that is the case, then it sounds like you're on the right track,
and you only need to adjust the driver to the one that Arjen
suggested.
Do you know roughly when this unit was manufactured? (Based on the
HCL, I would have guessed megatec as
Citeren Charles Lepple clep...@gmail.com:
Now that you mention the cypress_m8 driver again, I remember that, but
I also don't put much stock in VID:PID combinations these days, since
it is becoming more common for companies to borrow them from other
well-known companies.
This VID:PID is
Citeren Thomas Gutzler thomas.gutz...@gmail.com:
So when the batteries are critical, the master
- sends out FSD to all slaves and touches POWERDOWNFLAG
- waits for slaves to disconnect or max HOSTSYNC seconds to pass
- waits another FINALDELAY seconds
- executes its SHUTDOWNCMD, which
- stops
Citeren Thomas Gutzler thomas.gutz...@gmail.com:
Thanks for your very tutorial email. It helped a lot.
I have moved my master monitor to the nfs machine and setup upsmon on
all other machines.
Good. That is the most robust setup, short of having everything
powered from one huge UPS.
My
Citeren Thomas Gutzler thomas.gutz...@gmail.com:
My setup is this: I have 6 computers on 2 UPSs (3 each). Boths UPSs have
equal power ratings but the load on the slave is less. They are both
connected to and monitored by the same computer (I call it monitor); one
UPS is configured as master
Citeren Thomas Gutzler thomas.gutz...@gmail.com:
They're also on the same bus ('Bus 003 Device 063' and 'Bus 003 Device
064')
Since there is no flag for manufacturer,
There is. See 'man 8 usbhid-ups' for all regular expressions that you
can use to identify units.
I did that, but all I could
Citeren Nick Warr n...@mobilia.it:
How is the driver failing?
It says there's no Megatec protocol UPS on that port more or less.
Could you run the driver in debug mode and post the (gzip'ed) logs as
an attachment?
/path/to/megatec -DDD -a upsname
The upsname should be the name as
Citeren Nick Warr n...@mobilia.it:
[...]
Attempting to detect the UPS...
Sending Q1 command...
Wrong answer to Q1 command.
5 out of 5 detection attempts failed (minimum failures: 2).
Megatec protocol UPS not detected.
I was already afraid that we would get this result. We need a more
Citeren Thomas Jarosch thomas.jaro...@intra2net.com:
On Monday, 16. November 2009 13:57:11 Arnaud Quette wrote:
looking at the compat list, there is no specific entries for CS...
should I create one or is the Back-UPS USB entry sufficient?
I think the Back-UPS USB entry is fine. If the
Citeren Thomas Gutzler thomas.gutz...@gmail.com:
[...]
Strangely, vendor is '0x0463 MGE UPS Systems' for both.
Eaton is now the owner of what was formerly known as MGE Office
Protection Systems, which in turn is part of what used to be known as
MGE.
They're also on the same bus ('Bus
Citeren Bob Blackwell rc.blackw...@yahoo.ca:
I've just upgraded from r1865 to r2103. After doing so Input voltage
for an APC RS900 no longer appears on the web tools graph. Instead
of seeing a bar indicating Input Voltage the words Not Supported
appears. Why does the graph no longer report
Citeren Justin Piszcz jpis...@lucidpixels.com:
To find the problem, check the list for my thread DP55KG, you should
run a debug kernel and grab the usbmon output and report it to the
list.
Also stop nut and run each service manually with -D to see
what is happening within nut,
Citeren Justin Piszcz jpis...@lucidpixels.com:
Is it possible that a different USB Chip may act differently causing
this problem? As I noted CD/DVD (USB) and all other USB devices
function properly.
This may be due to the fact that we reconnect, instead of retry on
many signs of
Citeren BERSIHAND Christophe christophe.bersih...@icm46.org:
/lib/nut/megatec -a infosec returns
Network UPS Tools 2.2.1- - Megatec protocol driver 1.5.13 [megatec]
Carlos Rodrigues (c) 2003-2007
Megatec protocol UPS detected.
This UPS has an unsupported combination of battery voltage/number
Citeren Charles Lepple clep...@gmail.com:
could this be a result of setting pollfreq too low?
http://article.gmane.org/gmane.comp.monitoring.nut.user/5043
If this is not how pollfreq works, then I stand corrected - but if
the device is fully polled once every 30 seconds, and a power outage
Citeren Justin Piszcz jpis...@lucidpixels.com:
Even without the poll option, the error persists, but it takes
longer to trigger (3-5 minutes vs. 1-2 minutes @ 5 second follreq)
Have you also tried setting
pollinterval = 10
in ups.conf, to increase the polling interval for this UPS?
If
Citeren Alan Stern st...@rowland.harvard.edu:
Is there anything else I can do on my end? Or is this with the nut
developers at this point?
Well, there's nothing the kernel developers can do about it. :-)
The nut developers should try to follow up on the anomalies I found in
the usbmon
Citeren Jean Delvare kh...@linux-fr.org:
I'm testing it now. The new driver indeed shows new commands:
test.battery.start.deep - Start a deep battery test
test.battery.start.quick - Start a quick battery test
test.battery.stop - Stop the battery test
Good. You seem to be running the latest
Citeren Jean Delvare kh...@linux-fr.org:
Now the good news: the battery test command appears to work!
That's good to hear.
The test.battery.start.quick command behaves exactly as when using
APC's own software. The battery is being tested for a few seconds, then
the UPS returns online, and
Citeren Arjen de Korte nut+us...@de-korte.org:
After that I couldn't issue a test.battery.start.deep command again,
nothing happened when I tried. test.battery.start.quick still works
though.
Weird. I have no idea why that happens.
I just recalled that some UPSes will refuse to run a deep
Citeren Jean Delvare kh...@linux-fr.org:
PS Also, be advised that running deep discharge tests wear out your
battery, so you should only run these once every three to six months
(at most).
Thanks for the hint. I didn't intend to use it again any time soon
anyway. I presume it is essentially
Citeren Jean Delvare kh...@linux-fr.org:
Arnaud, Arjen, anything else I can do to help? The USB sniffer I'm
using is a shareware and I have only 11 days of use left. If you need
more captures, or different decoding, or any additional data, please
let me know quickly.
Would it be difficult to
Citeren Mathieu Brèthes math...@microsystem.fr:
Is it possible to add the Unitek Alpha 500 isx to the list of
working UPS? I have tried it this afternoon on one of our machines
and it is detected allright using the megatec_usb driver.
We would like to see the output of 'upsc' to see the
Citeren Kiss Gabor (Bitman) ki...@ssg.ki.iif.hu:
I have to simulate a behaviour of a real UPS. The physical model
contains an extra attribute: the charging current that needed to compute
recharge time and actual battery charge during the recharge process.
Can we call this variable
Citeren Алексей lesovsky...@uzps.mh.ru:
I have some problem when updating NUT. I have server with 4 UPS connected.
When I starting upsdrv and upsd and after sometime (1-2 minutes) I can't get
data from ups's
# upsc a...@localhost battery.type
Error: Data stale
and errors in
Citeren Kiss Gabor (Bitman) ki...@ssg.ki.iif.hu:
I played a bit with dummy driver in repeater mode.
It is the concept what I need.
Please explain what concept you need.
Unfortunately I found that if connection to another upsd gets broken
the driver does not try to repair it.
Depending on
Citeren Lindsey Chesnutt mrchesn...@gmail.com:
I've attached the requested output.
Although it didn't make it to the list (because we don't allow
attachments larger than 40 kB), I received it directly.
0.272003 HID descriptor, method 1: (9 bytes) = 09 21 10 01 00 01 22 c9
01
Citeren Vitor Choi Feitosa vc...@vchoi.org:
You're right. Brazil's voltage standard is 110v in some cities, 220v in most
and always 60hz. About the ups, it has a big red label stating use only on
220-240V. I really liked your input, so don't get me wrong here: as this
product was bought (in
Citeren Arnaud Quette arnaudque...@eaton.com:
please, keep the list cc'ed since other might interested in (either the
solution, or their 2 cents to the discussion). Moreover, knowing that
I'm not an author of the megatec / blazer drivers, things might be
obvious to these guys and not to me...
Citeren Chris Abel ca...@wildwood.edu:
Network UPS Tools - Tripp Lite OMNIVS / SMARTPRO driver 0.20 (2.4.1)
Warning: This is an experimental driver.
Some features may not function correctly.
Error: UPS [Tripp-Lite] is for driver usbhid-ups, but I'm tripplite_usb!
You failed to update the
Citeren Chris Abel ca...@wildwood.edu:
When using the tripplite_usb driver I get the same thing:
Checking device (09AE/0001) (001/002)
- VendorID: 09ae
- ProductID: 0001
- Manufacturer: TRIPP LITE
- Product: TRIPP LITE UPS
- Serial Number: unknown
- Bus: 001
Trying to match device
Device does
Citeren vk v...@union-metall.ru:
I have a nut 2.4.1 on FreeBSD 7.1 i386. UPS model is IPPON smart smart
power pro 2000. When i try to see battery charge, in output it have
not such variable, and i can't control other servers (Win2k3 + WinNUT)
because they not knows about current battery
Citeren Chris Abel ca...@wildwood.edu:
Although I do have that tag in my ./configure, I do not have the directory
/lib/nut after running make install. I have a lot of errors after running
make and make install. All related to snmp-ups.c
In that case, try if adding
--without-snmp
to the
Citeren Chris Abel ca...@wildwood.edu:
Am I the only one that has trouble compiling this with Ubuntu?
You clearly have a problem with control characters that are being
added somehow. Maybe it's the mail reader your using or some obscure
character set, I don't know. The attached shell
Citeren Chris Abel ca...@wildwood.edu:
I have attached my config.log.
You have some strange characters in the ./configure line. Please try
again with the following:
./configure --with-user=ups \
--with-group=nut\
--sysconfdir=/etc/nut
Citeren Arnaud Quette aquette@gmail.com:
strange indeed. the data is there, and now know.
I've made a minor fix (r1955).
please test it and tell me back if input.transfer.reason appears now.
No, it won't. The 'input.transfer.reason' value is set through the
VRANGE and FRANGE status
Citeren Brian Hoover bhoo...@viengineering.com:
No I just meant that I could not communicate to my APC UPS unless I
had the config in hyperterminal the way I stated, and it would not
respond to any command until I sent “Y”.
The protocol 'documentation' you're referring to is meant to aid
Citeren Jon Bendtsen jbendt...@laerdal.dk:
NUT cgi started to report the battery at 100% without i remember
doing anything.
It could be that the UPS has performed an automatic battery test or
runtime calibration in the mean time (which is not unusual for many
higher end devices).
Note
Citeren Svein Skogen (listmail account) svein-listm...@stillbilde.net:
I've set up my ups solution with a dedicated box (laptop with its own
powersupply) connected to the ups, and have set up upsmon.conf to use a
customized script (SHUTDOWNCMD
/usr/local/upsmonitor-files/shutdown.sh) that shuts
Citeren Svein Skogen (listmail account) svein-listm...@stillbilde.net:
Read the section on POWER VALUES in 'man 8 upsmon'. You probably should
assign the UPS a 'power value' of 0 (zero) on the laptop that is
monitoring it (but isn't powered by it).
if it's a value of 0, will it still invoke
Citeren Antoine Gatineau antoine.gatin...@alcatel-lucent.com:
I am facing some serious issues on customer's site.
I looked around on the web and in the archives but didn't find anything. I
hope you can help me.
Here is my configuration :
OS :RHES 4.7
NUT : 2.2.0
NUT-CLIENT : 2.2.0
Hardware :
Citeren Maurice Volaski mvola...@aecom.yu.edu:
upslogx(LOG_ERR, [%s] %s: Error in packet: %s,
This is a different message from what you reported before. These
where logged with 'nut_snmp_get' in them and these lines should now
be gone
(unless running in debug mode 2 or higher).
What
Citeren David Mohr damaili...@mcbf.net:
just wanted to let you know that I have two belkin F6C-1250-TW-RK
UPSes which work just fine with nut. I made this small patch so that
nut recognizes the usb device id.
Thanks for the patch! I committed the change for the belkin-hid
subdriver (the
Citeren Maurice Volaski mvola...@aecom.yu.edu:
This mib used to work, so is there a way to go back to the version
prior to this one without downgrading the whole package?
yes, only take the snmp-ups driver from the previous working release.
2.2.2 and 2.0.5 also complain but with fewer
Citeren Maurice Volaski mvola...@aecom.yu.edu:
This mib used to work, so is there a way to go back to the version
prior to this one without downgrading the whole package?
When did this stop working (from which version to nut-2.4.1 did you
upgrade)? The last changes to the IETF are made
Citeren vk v...@union-metall.ru:
gate# /usr/local/libexec/nut/blazer_usb - -a IPPON
Network UPS Tools - Megatec/Q1 protocol USB driver 0.03 (2.4.1)
debug level is '4'
Checking device (0665/5161) (/dev/usb1//dev/ugen0)
- VendorID: 0665
- ProductID: 5161
- Manufacturer: Cypress Semiconductor
Citeren vk v...@union-metall.ru:
Support for libusb is 'experimental' at best in FreeBSD and depending
on the version you're using, 'unusable'. You may try if adding a small
delay between sending a command and reading back the reply helps (YMMV):
--- trunk/drivers/blazer_usb.c (revision
To be able to calibrate the voltage conversions for the powerpanel
driver (binary mode) I need some startup logs for the PowerPanel Plus
(Windows) program that is provided by CyberPower. Preferably logs
created with the following tool:
Citeren Sergey s_...@mail.ru:
[...]
But, to switch off the electric power
After 20 min:
--
$upsc usb
..skip...
battery.charge: 100
battery.temperature: 36.8
battery.voltage: 23.9
input.voltage: 0.0
output.voltage: 220.4
ups.load: 24.7
ups.status: OL
Citeren Jon Bendtsen jbendt...@laerdal.dk:
I have a HP R3000 XR UPS which NUT never says is at 100% battery.
It seems stuck in 98 or 99 . something percentage.
Please mention the driver you're using when asking for help.
How accurate should i expect the reports to be? All my other UPSes
Citeren vk v...@union-metall.ru:
Hi! There is continue of my story with Ippon smart power 2000 and nut,
i'm enable usb in kernel and nut give following information:
gate# cat ups.conf
[IPPON]
driver = megatec_usb
port = /dev/ugen0
vendorid = 0665
productid = 5161
subdriver
Citeren benjamin thielsen bthiel...@safarivideonetworks.com:
working voltage graph:
[ups2]
driver = usbhid-ups
port = auto
[...]
battery.voltage: 27.7
battery.voltage.nominal: 24.0
This looks normal.
non-working voltage graph:
[ups4]
driver = snmp-ups
port = ups4
Citeren benjamin thielsen bthiel...@safarivideonetworks.com:
aha - thank you, that seems to have done the trick. i suppose that
dividing by zero would also explain the floating point error.
Yes. That tipped me off that there might be something wrong in the
values reported by the UPS.
Citeren Alexander Gordeev lasa...@lvk.cs.msu.su:
Please post the output of
/path/to/megatec_usb -u root -DDD -a IPPON
here. If this fails to connect to your UPS, chances are that you
haven't prepared your kernel to allow the userspace driver to bind
to the USB device. In that case,
Citeren vk v...@union-metall.ru:
Hi friends! It is not any answer to my previous letter about problem
with nut 2.4.1 and ippon smart power 2000 UPS with megatec_usb driver.
Maybe any additional information needed? Please help, any required
info i get.
Please post the output of
Citeren Anton E. Panchenko p...@chernigovka.org:
[...]
upsshed-cmd
#!/bin/sh
MSG=The UPS is running on battery about 2 minutes, doing force shutdown
case $1 in
fsd)
logger -t upssched-cmd $MSG
/sbin/upsmon -c fsd
;;
*)
logger -t upssched-cmd ERROR!! $0
Citeren Charles Lepple clep...@gmail.com:
ups.status:
The ups.status value is problematic - it should include at least OL
or OB. Not sure whether it is due to Protocol 4-related changes, or
the aforementioned timeout.
The above is due to a problem with calculation of the size of reports
Citeren Charles Lepple clep...@gmail.com:
The above is due to a problem with calculation of the size of reports in
libhid.c that was fixed more than a year ago. This fix requires nut-2.2.2 or
newer. For many USB devices, anything earlier than that may mean that they
run into this limitation
Citeren Rob MacGregor rob.macgre...@gmail.com:
I have a similar question to this as well, in that I have my server set up
using NUT with a SOLA-330 (working nicely!) and my desktop is using an APC
BackUPS-300 (this model has no serial/USB comms) as the SOLA APC are rated
the same, I was
Citeren Dr. Madhurjya P. Bora mpb...@yahoo.com:
I need to set up machine as slave which will act as a master to
some subordinate clients. The machine is question is a master node a
parallel cluster which I want it to act as a master for the
computing nodes but set itself as a slave with a
Citeren Vedran Furač vedr...@vedranf.mine.nu:
Where is megatec-mustek file?
It should be created by the driver, which apparently isn't running.
Either it isn't started at all, fails to detect the UPS or isn't
running with the proper permissions.
[snip]
dstate_init: sock
Citeren Gene Heskett gene.hesk...@gmail.com:
That seems to work, as in doesn't exit even if I run a second invocation of
usbhid-ups -a myups, both show up at the bottom of htop's listing, and both
responded to a kill from htop.
The output was:
[r...@coyote /]# usbhid-ups -a myups
Network UPS
Citeren Rene Bartsch m...@bartschnet.de:
I just reinstalled a current SVN and model is Smart-UPS, now. :)
Good.
But I also realized that upsrw can only set battery.date and
ups.id but nothing else. I'd
really appreciate to have the capability to set ups.test.interval
at least. ;)
Maybe
Citeren Brother Railgun of Reason ala...@caerllewys.net:
Oops, looking at the code I saw this isn't a warning, but a (fatal) error
instead (this was not one of the most descriptive error messages I ever
wrote). I now recall that this value is OS dependent, so you probably
want/need to limit
Citeren Rene Bartsch m...@bartschnet.de:
Command: upsc su900i
-- snip
---
battery.alarm.threshold: 0
battery.charge: 100.0
battery.charge.restart: 10
battery.date: 11/02/01
battery.runtime: 4440
Citeren Rene Bartsch m...@bartschnet.de:
Command: /lib/nut/apcsmart -a su900i -D
- snip
-
Network UPS Tools - APC Smart protocol driver 2.00 (2.4.1)
APC command table version 2.0
debug level is '5'
Citeren Brother Railgun of Reason ala...@caerllewys.net:
babylon4:root:/opt/nut:24 start
Network UPS Tools - UPS driver controller 2.4.1
Network UPS Tools - BCMXCP UPS driver 0.21 (2.4.1)
RS-232 communication subdriver 0.17
Connected to UPS on /dev/tty00 with baudrate 19200
OK, the driver is