> On 17 Jan 2018, at 2:27 pm, Charles Lepple <clep...@gmail.com> wrote:
>
> On Jan 16, 2018, at 6:07 PM, James Whitwell <j...@momento.com.au> wrote:
>>
>> This might be a simple thing to fix, but I can’t figure it out. We replaced
>> the battery for t
Hi,
This might be a simple thing to fix, but I can’t figure it out. We replaced
the battery for the first time in our Eaton 5PX a couple of weeks ago, but we
haven’t been able to clear the “ups.alarm: replace battery!” status.
Details of our installation are:
OS: Debian 6
NUT version: 2.7.4
Hi
I have installed nut 2.6.5-6 using the msi installer, but during the install
popped up a box asking me to manually install libusb0.dll
The msi package doesn't seem to contain the libusb0.dll, the question is, where
do I get it from?
Thx
___
been
chmod to 777 with no difference.
Cheers,
James
Date: Mon, 27 Apr 2015 16:04:34 +0200
From: ro...@rogerprice.org
To: nut-upsuser@lists.alioth.debian.org
Subject: Re: [Nut-upsuser] upssched setup
On Mon, 27 Apr 2015, James Hammond wrote:
Roger, I did and it didnt work.
Aha!, what does
,
James
Date: Mon, 27 Apr 2015 21:25:45 +0100
From: n...@dana.org.uk
To: nut-upsuser@lists.alioth.debian.org
Subject: Re: [Nut-upsuser] upssched setup
Hi,
The exec is returning 126 - Command invoked cannot execute. A
permission or command not executable problem..
Are you sure
Roger,
Yes thanks I have been using your site as a guide (excellent writeup), trying
to work out the difference between OpenSUSE and Ubuntu.
I will re-visit this tomorrow and try to tighten up security.
Cheers,
James
Date: Mon, 27 Apr 2015 23:06:37 +0200
From: ro...@rogerprice.org
To: nut
upssched-cmd.sh
I have the command pointing at the correct place:
unifi@unifi:~$ command -v upsmon/sbin/upsmon
Any help appreciated. All I am looking to do is shutdown this master upsd and
send shutdown requests to 2 other slaves after 10 mins of the UPS going onto
battery.
Cheers,
James
Roger,
I did and it didnt work.
Hence why I was trying to run just the shell script manually. I am not sure if
this works though with the timer defined in it?
Cheers,
James
Date: Mon, 27 Apr 2015 15:03:44 +0200
From: ro...@rogerprice.org
To: nut-upsuser@lists.alioth.debian.org
Subject: Re: [Nut
Upgrading to 2.7.3 and using the nutdrv_qx driver and everything is talking now
between 3 devices.
I will need to test shutdown when I get home, but thanks for the excellent
support.
Cheers,James
Subject: Re: [Nut-upsuser] Fry's Electronics UPS...
From: clep...@gmail.com
Date: Thu, 23 Apr
version of NUT.
If this does not help,try running the driver with at least 'subdriver',
'vendorid' and 'productid'options specified. Please refer to the man page for
details about these options(man 8 blazer).
Is there anything else I can try or just forget it?
Cheers,
James
, 2013 3:07 AM
To: James HORLEY
Cc: nut-upsuser list
Subject: Re: [Nut-upsuser] infosec e4
On Aug 26, 2013, at 6:22 AM, James HORLEY wrote:
I've download again nut source today from
https://github.com/networkupstools/nut/tree/voltronic-driver; and try
compiliing the voltronic-driver
,
-Message d'origine-
From: James HORLEY
Sent: Thursday, August 01, 2013 4:40 PM
To: nut-upsuser list
Subject: Re: [Nut-upsuser] infosec e4
I'm pretty sure, I've install pkg-config, but I will check it monday after
my holliday.
This is my test steps:
- Shutting down nut-client (upsmon
using upssched to shutdown server after 15mn on battery, the
shutdown -h +0 isn't enough to shutdown ups.
Do I need to use upscmd in order to shutdown ups, or is there another way?
Best regards,
-Message d'origine-
From: Charles Lepple
Sent: Thursday, August 01, 2013 2:19 AM
To: James
2:25 AM
To: James HORLEY
Cc: nut-upsuser list
Subject: Re: [Nut-upsuser] infosec e4
On Jul 31, 2013, at 9:07 AM, James HORLEY wrote:
I’m wondering if what I have done is good :
# get the source from github on my computer
# autogen.sh
# name=nut
#
./configure --prefix
and put it
on the server? Or should I do a package of the whole nut (binary, conf etc...)
Best regards,
From: hyo...@gmail.com
Sent: Monday, July 29, 2013 1:34 AM
To: James HORLEY
Subject: Re: [Nut-upsuser] infosec e4
You could try voltronic driver
https://github.com/networkupstools/nut/tree
Hi,
Sorry for my poor english but it isn’t my native language.
I’m testing an infosec E4 with nut-2.6.4-2.3 on Proxmox ve 3.0 (based on
debian wheezy). The drivers that match this ups, is blazer_usb.
Btw, I have try nut-2.6.5 with unstable repository from wheezy, but it still
doesn’t fully
On Tue, Jul 24, 2012 at 3:18 AM, fredericb...@eaton.com wrote:
Hello Jim,
Can you send your configuration files please (hide your password).
Regards,
Fred
--
Eaton Opensource Team - http://opensource.eaton.com
I hope I'm sending the right stuff. It's out of the box setup. I didn't
Commander 2000 for $990 last
year. I think I had NUT running on Ubuntu 11.04, but didn't find I
needed it, and repurposed the cable.
P.S. I've looked for but not found a NUT IRC channel. Does one exist,
and if so, where can I find it?
No idea. Quozl on freenode #olpc.
--
James Cameron
http
On Wed, Mar 07, 2012 at 05:25:06PM +1100, Matthew Cengia wrote:
On 2012-03-07 16:46, James Cameron wrote:
[...]
3. Can anybody recommend a UPS that meets the following specs:
* Works with the aforementioned version of NUT, either via USB or
RS232
* Is ideally rack
processed the
data.
http://quozl.linux.org.au/speedo/
--
James Cameron
http://quozl.linux.org.au/
___
Nut-upsuser mailing list
Nut-upsuser@lists.alioth.debian.org
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser
, sometimes it will
connect, other times it won't.
From the thread: Re: [Nut-upsuser] USB CyberPower
---
Hi James,
I've worked extensively on getting a similar CyberPower UPS (same IDs) to play
well with nut.
The conclusion I ultimately came
I have a ups that doesn't always (sometimes it does) load NUT right.
I use Gentoo:
* sys-power/nut
Latest version available: 2.6.0-r1
Latest version installed: 2.6.0-r1
Size of files: 1,663 kB
Homepage: http://www.networkupstools.org/
Description:
On 11-09-29 12:22 PM, Mark Butsch wrote:
Hello,
I am new to NUT (running Ubuntu Lucid (10.04) and NUT 2.4.3 (from the Ubuntu
package).
I have been trying to use an APC Back-UPS ES 750, but when running the Shutdown
Design test it doesn't cause my computer to power back on. It appears that it
the udev service before calling upsdrvctl in
/etc/init.d/ups-monitor, but the driver still failed to load. I will
try some more tomorrow.
In the mean time, if anybody has run into this before, I would love some
pointers.
James
___
Nut-upsuser mailing
shutdown - this also didn't work.
Does anyone have any ideas on why the shutdown command is failing when
run as part of the halt process? Or do you have any pointers on
debugging the halt process?
Thanks,
James
___
Nut-upsuser mailing list
Nut-upsuser
to change state when the
contact opens
Thx
-Original Message-
From: Charles Lepple [mailto:clep...@gmail.com]
Sent: Tuesday, June 21, 2011 7:18 AM
To: James Smith
Cc: 'nut-upsuser@lists.alioth.debian.org'
Subject: Re: [Nut-upsuser] Using NUT to detect a normally closed circuit opening
On Jun
...@gmail.com]
Sent: Tuesday, June 21, 2011 7:18 AM
To: James Smith
Cc: 'nut-upsuser@lists.alioth.debian.org'
Subject: Re: [Nut-upsuser] Using NUT to detect a normally closed circuit opening
On Jun 20, 2011, at 2:09 PM, James Smith wrote:
I have a temperature sensor (normally closed) that opens when
to detect a normally closed circuit opening
Citeren James Smith james.sm...@jofco.com:
I now have everything in place and I get an email when the temp sensor
opens
Question - what do I set so the system doesn't shut down when the
sensor stays open?
The system will only shutdown if you have an OB
$ sudo /usr/sbin/upsd -
Network UPS Tools upsd 2.4.3
0.00 listen_add: added ::1:3493
0.84 listen_add: added 127.0.0.1:3493
0.000102 setuptcp: try to bind to 127.0.0.1 port 3493
0.000185 listening on 127.0.0.1 port 3493
0.000204 setuptcp: try to bind
this username and password?
--
James Cameron
http://quozl.linux.org.au/
0.00 debug level is '3'
0.041776 Checking device (1D6B/0001) (002/001)
0.041991 - VendorID: 1d6b
0.042031 - ProductID: 0001
0.042054 - Manufacturer: Linux 2.6.35-27-generic uhci_hcd
or resource busy)
Successfully reconnected
... and this repeats periodically.
--
James Cameron
http://quozl.linux.org.au/
Bus 001 Device 004: ID 0665:5161 Cypress Semiconductor USB to Serial
Device Descriptor:
bLength18
bDescriptorType 1
bcdUSB 1.10
On 12/29/10 04:19, Kjell Claesson wrote:
Hi James,
$ sudo upsdrvctl start
Network UPS Tools - UPS driver controller 2.4.3
Network UPS Tools - Generic HID driver 0.34 (2.4.3)
USB communication driver 0.31
Using subdriver: CyberPower HID 0.3
OK, the driver seems to start.
But have you
$ sudo upsdrvctl start
Network UPS Tools - UPS driver controller 2.4.3
Network UPS Tools - Generic HID driver 0.34 (2.4.3)
USB communication driver 0.31
Using subdriver: CyberPower HID 0.3
$ sudo upsc my...@localhost
Error: Driver not connected
___
On 11/22/10 03:34, Arjen de Korte wrote:
Citeren James bjloc...@lockie.ca:
I have two UPSs, one is not connected to a computer.
I am looking for a gadget that I can plug in to the other one so I can
see the time remaining without a computer.
Since you don't mention the make and model
On 11/22/10 03:34, Arjen de Korte wrote:
Citeren James bjloc...@lockie.ca:
I have two UPSs, one is not connected to a computer.
I am looking for a gadget that I can plug in to the other one so I can
see the time remaining without a computer.
Since you don't mention the make and model
but not serial ports.
James
___
Nut-upsuser mailing list
Nut-upsuser@lists.alioth.debian.org
http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser
I have two UPSs, one is not connected to a computer.
I am looking for a gadget that I can plug in to the other one so I can
see the time remaining without a computer.
___
Nut-upsuser mailing list
Nut-upsuser@lists.alioth.debian.org
on Linux.
If you really do want to continue with Dynamix then check out the manufacturers
site. There is a model which has a real serial port that will probably be ok.
Regards,
James.
___
Nut-upsuser mailing list
Nut-upsuser@lists.alioth.debian.org
On 07/14/10 11:27, Arjen de Korte wrote:
the UPS should power off(and restart when the power comes back
Can I set any UPS to only provide power after the battery is charged
to a certain level?
Or better yet, a certain length on consecutive time when the power has
been on.
I'd be worried
Why is battery.mfr.date not a date?
Why is there no device.serial?
Are they both errors on CyberPower's part?
$ /usr/local/ups/bin/upsc cp550...@localhostbattery.charge: 100
battery.charge.low: 10
battery.charge.warning: 20
battery.mfr.date: CPS
battery.runtime: 960
battery.runtime.low: 300
I used VirtualBox to run the Windows software and now nut works.
It might be a coincidence. :-(
I rebooted once and didn't run VirtualBox and nut works.
We'll see if it breaks.
___
Nut-upsuser mailing list
Nut-upsuser@lists.alioth.debian.org
On 05/11/10 20:56, James wrote:
I used VirtualBox to run the Windows software and now nut works.
It might be a coincidence. :-(
I rebooted once and didn't run VirtualBox and nut works.
We'll see if it breaks.
I was playing around with different options.
I did use these:
./configure
I was getting:
Can't claim USB device [0764:0501]: could not detach kernel driver from
interface 0: Operation not permitted
so I manually installed the udev rules the source (I installed the
Gentoo ebuild).
I am now getting:
# upsdrvctl start
Network UPS Tools - UPS driver controller 2.4.3
On 05/10/10 08:31, Charles Lepple wrote:
On Mon, May 10, 2010 at 1:49 AM, Jamesbjloc...@lockie.ca wrote:
I was getting:
Can't claim USB device [0764:0501]: could not detach kernel driver from
interface 0: Operation not permitted
so I manually installed the udev rules the source (I installed
On 05/10/10 14:37, Jason Englander wrote:
On Mon, 10 May 2010, James wrote:
Network UPS Tools - UPS driver controller 2.4.3
Network UPS Tools - Generic HID driver 0.34 (2.4.3)
USB communication driver 0.31
Using subdriver: CyberPower HID 0.3
libusb_get_report: could not claim interface 0
# export USB_DEBUG=5
# /usr/local/ups/bin/usbhid-ups -a CP550SLG -D
Network UPS Tools - Generic HID driver 0.34 (2.4.3)
USB communication driver 0.31
0.00 debug level is '5'
0.000426 upsdrv_initups...
usb_set_debug: Setting debugging level to 5 (on)
usb_os_init: Found USB
On 05/10/10 22:09, Charles Lepple wrote:
On Mon, May 10, 2010 at 8:35 PM, Jamesbjloc...@lockie.ca wrote:
On 05/10/10 14:37, Jason Englander wrote:
On Mon, 10 May 2010, James wrote:
Network UPS Tools - UPS driver controller 2.4.3
Network UPS Tools - Generic HID driver 0.34 (2.4.3)
USB
On 05/10/10 23:25, Charles Lepple wrote:
On Mon, May 10, 2010 at 11:02 PM, Jamesbjloc...@lockie.ca wrote:
On 05/10/10 22:09, Charles Lepple wrote:
On Mon, May 10, 2010 at 8:35 PM, Jamesbjloc...@lockie.cawrote:
[...]
0.000663 failed to claim USB device: could not claim
Charles Lepple wrote:
On Sep 9, 2009, at 8:36 AM, James Moody wrote:
All of this work is being done on the system that has the UPS - I'm
not trying to do any network monitoring yet. The symptom is that when
I try to use 'upsc' I get the failure message Error: server
disconnected
Does the battery voltage match the front panel? The specs on the
website say 4x 12V batteries, but that could be in a 2x2 arrangement
to give 24V.
there is no voltage information on the front panel so i am not sure whats going
on there.
Was upsc actually showing two copies of these values,
On Mon, Aug 10, 2009 at 10:26:41PM -0400, Charles Lepple wrote:
[please keep this thread on-list - that way other people can reference
it later.]
On Aug 10, 2009, at 10:24 PM, James Erickson wrote:
Please run /lib/nut/usbhid-ups -a cyberpower -u root -x
productid=0601, and if we need
On Mon, Aug 10, 2009 at 10:26:41PM -0400, Charles Lepple wrote:
[please keep this thread on-list - that way other people can reference
it later.]
On Aug 10, 2009, at 10:24 PM, James Erickson wrote:
Please run /lib/nut/usbhid-ups -a cyberpower -u root -x
productid=0601, and if we need
On Mon, Aug 10, 2009 at 10:26:41PM -0400, Charles Lepple wrote:
[please keep this thread on-list - that way other people can reference
it later.]
On Aug 10, 2009, at 10:24 PM, James Erickson wrote:
Please run /lib/nut/usbhid-ups -a cyberpower -u root -x
productid=0601, and if we need
i own a CyberPower OR2200LCDRM2U and was wondering if any nut drivers
support this ups. none i have tried have worked although usbhid-ups did
tell me that the productid=0601 was not supported yet. i see in the
compatability list on the nut website that the PR2200 is supported with
the
On Sun, Aug 09, 2009 at 06:38:32PM -0400, Charles Lepple wrote:
From: James Erickson
Date: August 9, 2009 6:17:51 PM EDT
To: Charles Lepple
Subject: Re: [Nut-upsuser] CyberPower OR2200
On Sun, Aug 09, 2009 at 03:46:26PM -0400, Charles Lepple wrote:
On Aug 9, 2009, at 12:01 PM
.
upsc says this about the battery state:
battery.charge: 100
battery.charge.low: 10
battery.charge.warning: 30
battery.temperature: 34.9
battery.type: PbAC
battery.voltage: 54.6
battery.voltage.nominal: 48.0
thanks
James
___
Nut-upsuser mailing list
Nut
-Original Message-
From: Arjen de Korte [mailto:[EMAIL PROTECTED]
Sent: Wednesday, 17 September 2008 17:35
To: James Harper
Cc: nut-upsuser
Subject: Re: [Nut-upsuser] Access to internal UPS logs?
Citeren James Harper [EMAIL PROTECTED]:
It's a brand new UPS (3 weeks old
, so that it
wouldn't down the server in the event of failure, and no messages were
logged and the UPS continues reporting status (being graphed via mrtg).
Thanks
James
___
Nut-upsuser mailing list
Nut-upsuser@lists.alioth.debian.org
http
somewhere it would be useful to get access to them.
I just noticed that upsmon wasn't running, which would explain the
absence of anything useful in syslog.
My question about internal logs still stands though.
Thanks
James
___
Nut-upsuser mailing list
Nut
James
___
Nut-upsuser mailing list
Nut-upsuser@lists.alioth.debian.org
http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser
?
One more thing... if it helps, the usb info is:
Bus 003 Device 003: ID 03f0:1f0a Hewlett-Packard
James
___
Nut-upsuser mailing list
Nut-upsuser@lists.alioth.debian.org
http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser
status (Q1 command)...
UPS status: (245.1 245.0 245.1 035 50.1 13.3 25.0 1000
Charge: 90.0%
The charge is wrong, it's fully charged, but I guess that's what the
battvolts override is for.
Thanks, that was much less painful than I thought it was going to be.
James Andrewartha
62 matches