Re: [Nut-upsuser] problem with output voltage on a mustek ups

2008-03-08 Thread Carlos Rodrigues
On Fri, Mar 7, 2008 at 11:15 AM, Pedro Mendes Jorge [EMAIL PROTECTED] wrote: This output voltage is too low! I think power spikes may be better than using this voltage. Is this indicated by the UPS, or did you measure this voltage externally? Arjen has mentioned this before,

Re: [Nut-upsuser] problem with output voltage on a mustek ups

2008-03-07 Thread Pedro Mendes Jorge
Arjen de Korte wrote: [EMAIL PROTECTED] wrote: Do you mean the computer's power supply? But it is supposed to run on 220-230V not on 202V! Isn't this a problem? No. The mains voltage is specified within a 230V -15/+10%, since the voltage was harmonized within the EU. So a mains voltage

Re: [Nut-upsuser] problem with output voltage on a mustek ups

2008-03-07 Thread Pedro Mendes Jorge
Charles Lepple wrote: On Thu, Mar 6, 2008 at 6:22 AM, [EMAIL PROTECTED] wrote: Input Voltage 241.1 Output Voltage 202.0 nominal 220.0 ??? This output voltage is too low! I think power spikes may be better than using this voltage. Is this indicated by the

Re: [Nut-upsuser] problem with output voltage on a mustek ups

2008-03-06 Thread Arjen de Korte
My problem is that sometimes the UPS is running OK, but when the message UPS is trimming incoming voltage appears on knutclient (i.e. OL TRIM in nut), I have something like Input Voltage 241.1 Output Voltage 202.0 nominal 220.0 ??? This output voltage is too low! I

[Nut-upsuser] problem with output voltage on a mustek ups

2008-03-06 Thread pmjorge
Hi there I have a Mustek PowerMust 1000 USB using serial port /dev/ttyS0. I use nut 2.2.1 with the megatec driver on Debian Lenny (testing), running on an AMD64 X2. (I was using a Debian Etch as slave, but to keep it simple I turned it off) My problem is that sometimes the UPS is running OK,

Re: [Nut-upsuser] problem with output voltage on a mustek ups

2008-03-06 Thread pmjorge
Quoting Arjen de Korte [EMAIL PROTECTED]: My problem is that sometimes the UPS is running OK, but when the message UPS is trimming incoming voltage appears on knutclient (i.e. OL TRIM in nut), I have something like Input Voltage 241.1 Output Voltage 202.0 nominal 220.0

Re: [Nut-upsuser] problem with output voltage on a mustek ups

2008-03-06 Thread Arjen de Korte
[EMAIL PROTECTED] wrote: Do you mean the computer's power supply? But it is supposed to run on 220-230V not on 202V! Isn't this a problem? No. The mains voltage is specified within a 230V -15/+10%, since the voltage was harmonized within the EU. So a mains voltage of anything between 196 and

Re: [Nut-upsuser] problem with output voltage on a mustek ups

2008-03-06 Thread Charles Lepple
On Thu, Mar 6, 2008 at 6:22 AM, [EMAIL PROTECTED] wrote: Input Voltage 241.1 Output Voltage 202.0 nominal 220.0 ??? This output voltage is too low! I think power spikes may be better than using this voltage. Is this indicated by the UPS, or did you measure