Re: [Nut-upsuser] Support of amp; amp; amp; amp; quot; shutdown.returnamp; amp; amp; amp; quot; on a APC Back-UPS CS 500

2011-01-20 Thread Kevin
Kevin bakdong at gmail.com writes: on 19/01/2011 15:31 Arjen de Korte wrote: Please also post the output of 'upsc upsname' (see 'man 8 upsc') and 'upscmd -l upsname' (see 'man 8 upscmd') for both devices, so that we can see which commands are detected. APC Smart-UPS 1000 #

Re: [Nut-upsuser] Support of amp;amp; amp; amp; amp; quot; shutdown.returnamp;amp; amp; amp; amp; quot; on a APC Back-UPS CS 500

2011-01-20 Thread Kevin
Kevin bakdong at gmail.com writes: Sorry, this is the correct output for the Smart-UPS 1000 # clients/upsc apc1500 battery.charge: 100 battery.charge.low: 10 battery.charge.warning: 50 battery.mfr.date: 2007/07/07 battery.runtime: 6300 battery.runtime.low: 120 battery.temperature: 31.5

Re: [Nut-upsuser] Support of amp; amp; amp; amp; quot; shutdown.returnamp; amp; amp; amp; quot; on a APC Back-UPS CS 500

2011-01-20 Thread Arjen de Korte
Citeren Kevin bakd...@gmail.com: On the Smart-UPS 1000, all the instant commands do more or less what you would expect. Looking at the timers using upsc apc1500 I now see that: shutdown. load.off/load.off.delay both set the shutdown timer to 90, shuts down after 90 seconds It

Re: [Nut-upsuser] Support of amp; amp; amp; amp; amp; quot; shutdown.returnamp; amp; amp; amp; amp; quot; on a APC Back-UPS CS 500

2011-01-20 Thread Kevin
Arjen de Korte nut+users at de-korte.org writes: Citeren Kevin bakdong at gmail.com: return immediately switches to battery for a moment, sets both shutdown and startup to 90 seconds, sleeps after 90 seconds That is very odd. You could try what happens if you change the