[Nut-upsuser] Powercom BNT-800AP

2010-02-04 Thread cooleyr
While fundamentally working, I'm having a few issues with the driver...

The default voltage quads (for every model) are way off...  Showing
~95v when it should be ~117V.  I've changed the 4th/final coefficient
to +5.0, but haven't tested extensively (with fluctuating voltages).

The input/output voltage appears to be swapped _most of the time_.
When doing a battery test, or when unplugged, the input stays steady,
and the _output_ voltage reports a drop to ~15V.  OTOH, when the UPS
is shutdown, the ordering appears correct, as the input stays steady,
and the output shows ~5V.

For the above, the Powercom upsmon software appears to special-case
those ~5/15V results, and on the next update, report it as 0V.  I have
no idea how to even special-case the screwy input/output-swapping
behavior...


./powercom -a ups0 -DDD
Network UPS Tools - PowerCom protocol UPS driver 0.12 (2.4.1-2308)
   0.00 debug level is '3'
   0.001406 Flow control disable
   0.150003 Detected: BNT-other-500AP , 120V
   0.153986 Values of arguments:
   0.154001  manufacturer: 'PowerCom'
   0.154009  model name  : 'BNT-other-500AP'
   0.154015  serial number   : 'Unknown'
   0.154022  line voltage: '120'
   0.154029  type: 'BNT-other'
   0.154036  number of bytes from UPS: '16'
   0.154042  method of flow control  : 'no_flow_control'
   0.154051  validation sequence: '{{8,0},{8,0},{8,0}}'
   0.154059  shutdown arguments: '{{1,30},y}'
   0.154073  frequency calculation coefficients: '{0.000208,0.00}'
   0.154084  load percentage calculation coefficients:
'{1.447400,0.00,0.859400,0.00}'
   0.154101  battery percentage calculation coefficients:
'{5.00,0.326800,-825.00,0.465110,0.00}'
   0.154110  voltage calculation coefficients: '{0.954500,5.00}'
   0.305927 input.frequency   (raw data): [raw: 80]
   0.305966 input.frequency: 60.09
   0.305974 output.frequency   (raw data): [raw: 80]
   0.305987 output.frequency: 60.09
   0.305994 ups.load  (raw data): [raw: 0]
   0.306008 ups.load: 0.0
   0.306015 battery.charge (raw data): [raw: 197]
   0.306027 battery.charge: 100.0
   0.306035 input.voltage (raw data): [raw: 119]
   0.306048 input.voltage: 118.6
   0.306055 output.voltage (raw data): [raw: 26]
   0.306067 output.voltage: 29.8
   0.306079 STATUS: OB TEST
   0.306338 dstate_init: sock /var/state/ups/powercom-ups0 open on fd 5
   0.453868 input.frequency   (raw data): [raw: 80]
   0.453907 input.frequency: 60.09
   0.453914 output.frequency   (raw data): [raw: 80]
   0.453925 output.frequency: 60.09
   0.453931 ups.load  (raw data): [raw: 0]
   0.453944 ups.load: 0.0
   0.453950 battery.charge (raw data): [raw: 195]
   0.453961 battery.charge: 100.0
   0.453968 input.voltage (raw data): [raw: 119]
   0.453979 input.voltage: 118.6
   0.453986 output.voltage (raw data): [raw: 26]
   0.453997 output.voltage: 29.8
   0.454008 STATUS: OB TEST
   1.853474 new connection on fd 6
   2.457023 input.frequency   (raw data): [raw: 80]
   2.457070 input.frequency: 60.09
   2.457077 output.frequency   (raw data): [raw: 80]
   2.457088 output.frequency: 60.09
   2.457095 ups.load  (raw data): [raw: 0]
   2.457108 ups.load: 0.0
   2.457115 battery.charge (raw data): [raw: 191]
   2.457140 battery.charge: 95.0
   2.457147 input.voltage (raw data): [raw: 119]
   2.457159 input.voltage: 118.6
   2.457167 output.voltage (raw data): [raw: 25]
   2.457185 output.voltage: 28.9
   2.457197 STATUS: OB TEST
   4.456188 input.frequency   (raw data): [raw: 80]
   4.456240 input.frequency: 60.09
   4.456248 output.frequency   (raw data): [raw: 80]
   4.456259 output.frequency: 60.09
   4.456266 ups.load  (raw data): [raw: 0]
   4.456279 ups.load: 0.0
   4.456286 battery.charge (raw data): [raw: 193]
   4.456656 battery.charge: 100.0
   4.456673 input.voltage (raw data): [raw: 119]
   4.456686 input.voltage: 118.6
   4.456693 output.voltage (raw data): [raw: 119]
   4.456849 output.voltage: 118.6
   4.456978 STATUS: OL
   6.455365 input.frequency   (raw data): [raw: 80]
   6.455420 input.frequency: 60.09
   6.455428 output.frequency   (raw data): [raw: 80]
   6.455439 output.frequency: 60.09
   6.455445 ups.load  (raw data): [raw: 0]
   6.455458 ups.load: 0.0
   6.455465 battery.charge (raw data): [raw: 193]
   6.455476 battery.charge: 100.0
   6.455483 input.voltage (raw data): [raw: 119]
   6.455494 input.voltage: 118.6
   6.455500 output.voltage (raw data): [raw: 119]
   6.455511 output.voltage: 118.6
   6.455522 STATUS: OL

For anyone wondering, I wouldn't recommend these units to anyone else.
 A 400W dumb/personal UPS from 

[Nut-upsuser] (no subject)

2010-02-02 Thread cooleyr


___
Nut-upsuser mailing list
Nut-upsuser@lists.alioth.debian.org
http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser


[Nut-upsuser] (no subject)

2010-02-02 Thread cooleyr


___
Nut-upsuser mailing list
Nut-upsuser@lists.alioth.debian.org
http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser


Re: [Nut-upsuser] Compiling NUT static binaries

2009-05-19 Thread cooleyr
On Tue, May 19, 2009 at 2:21 PM, cool...@gmail.com wrote:


 I expect there's some libtool / gcc linking flag I'm ignorant of, or
 neglecting to use, but extensive trial and error has not found it.
 [-Xlinker] -all-static , -without-shared, -static-libtool-libs, etc. have
 not had any effect on the end binary.


Problem solved.

The ./configure script errors-out when LDxxx=-all-static is used,
with/without -Xlinker.   However, there's nothing actually wrong with using
the option on this or other systems... It's merely ./configure
brain-damage.

After running configure without the option, adding the -all-static option to
the LDFLAGS of each individual Makefile (in my case, just
nut-2.4.1/clients/Makefile) works perfectly.

I only hope my hours of neddless suffering helps someone.