[Sprinklerforum] Re: Standpipe NFPA14 2019

2024-05-10 Thread Rick Matsuda
Gosh, 73-feet is a long distance to drag fire hose from the valve at the exit door along the length of the rated exit passageway. If there’s no occupancy openings in the length of the exit passageway, then maybe you could ask the AHJ if he wants a hose valve at the inside end of the exit

[Sprinklerforum] Re: Standpipe NFPA14 2019

2024-05-10 Thread Steve Leyton
Do you have a hose connection on the 1st floor landing of the remote standpipe stairwell in addition to the one at the exit passageway door? And is there access to occupiable areas on the first floor from the passageway or stairwell? Obviously, two or more hose connections supplied by a feed

[Sprinklerforum] Re: [External]Re: ESFR Sprinklers and Antifreeze Solutions

2024-05-10 Thread Kyle . Montgomery
That data sheet is 13 years old. Does that all still apply today? -Kyle M From: José Gregorio Prada Rodriguez Sent: Thursday, May 9, 2024 7:29 AM To: Discussion list on issues relating to automatic fire sprinklers Subject: [External][Sprinklerforum] Re: ESFR Sprinklers and Antifreeze

[Sprinklerforum] Standpipe NFPA14 2019

2024-05-10 Thread Chris Wilson
To all, I have a 4 story building with 2 exit stairways I am installing a class I manual wet standpipe combination sprinkler system. The remote stair is on the interior of the building and has a rated exit passageway on the first floor that is 73' long. I am placing all hose valves on the