From: Chris Wilson
Sent: Monday, May 13, 2024 6:57 AM
To: Discussion list on issues relating to automatic fire sprinklers
Subject: [Sprinklerforum] Re: Standpipe NFPA14 2019
Steve,
Yes there is a hose connection at the first floor landing of the remote stand
pipe. Yes there is ac
ubject: [Sprinklerforum] Re: Standpipe NFPA14 2019
Do you have a hose connection on the 1st floor landing of the remote standpipe
stairwell in addition to the one at the exit passageway door? And is there
access to occupiable areas on the first floor from the passageway or stairwell?
Obviousl
Gosh, 73-feet is a long distance to drag fire hose from the valve at the exit
door along the length of the rated exit passageway.
If there’s no occupancy openings in the length of the exit passageway, then
maybe you could ask the AHJ if he wants a hose valve at the inside end of the
exit
Do you have a hose connection on the 1st floor landing of the remote standpipe
stairwell in addition to the one at the exit passageway door? And is there
access to occupiable areas on the first floor from the passageway or stairwell?
Obviously, two or more hose connections supplied by a feed