[Sprinklerforum] Re: Standpipe NFPA14 2019

2024-05-15 Thread Steve Leyton
nning | Training From: Chris Wilson Sent: Monday, May 13, 2024 6:57 AM To: Discussion list on issues relating to automatic fire sprinklers Subject: [Sprinklerforum] Re: Standpipe NFPA14 2019 Steve, Yes there is a hose connection at the first floor landing of the remote stand pipe. Yes there is ac

[Sprinklerforum] Re: Standpipe NFPA14 2019

2024-05-13 Thread Chris Wilson
ubject: [Sprinklerforum] Re: Standpipe NFPA14 2019 Do you have a hose connection on the 1st floor landing of the remote standpipe stairwell in addition to the one at the exit passageway door? And is there access to occupiable areas on the first floor from the passageway or stairwell? Obviousl

[Sprinklerforum] Re: Standpipe NFPA14 2019

2024-05-10 Thread Rick Matsuda
Gosh, 73-feet is a long distance to drag fire hose from the valve at the exit door along the length of the rated exit passageway. If there’s no occupancy openings in the length of the exit passageway, then maybe you could ask the AHJ if he wants a hose valve at the inside end of the exit

[Sprinklerforum] Re: Standpipe NFPA14 2019

2024-05-10 Thread Steve Leyton
Do you have a hose connection on the 1st floor landing of the remote standpipe stairwell in addition to the one at the exit passageway door? And is there access to occupiable areas on the first floor from the passageway or stairwell? Obviously, two or more hose connections supplied by a feed