I have a 4 story building with 2 exit stairways I am installing a class I 
manual wet standpipe combination sprinkler system. The remote stair is on the 
interior of the building and has a rated exit passageway  on the first floor 
that is 73' long. I am placing all hose valves on the main floor landings and 
one a the exit door of the exit passage way.

I am planning on calculating 500 gpm from the remote stand pipe and 250 for the 
2nd standpipe. The exit passage way hose connection will be fed by a  2/12 
lateral pipe fed from the  4" horizontal supply to the remote standpipe as it 
pass by the exit passageway.

Do I need to include an additional 250 gpm in my calcs at the hose valve at the 
exit passageway?

Thanks