It’s germane to NANOG. Just last week I visited a “data center” that uses a 
roll up generator and a cheater cord to power the racks. “Oh, this is safe”, 
they told me. “We have a policy that you must throw the main breaker before 
plugging in the generator. Since you have to open the garage door to wheel in 
the generator (!), you walk right by the switchgear and a sign that reminds you 
to throw the breaker.”

Code enforcement is on the way. :)

 -mel

On Aug 31, 2021, at 7:50 AM, Josh Luthman <j...@imaginenetworksllc.com> wrote:


Is this conversation really taking place on NANOG?

Don't backfeed power.  Got it.  Stupid people are going to be stupid, we won't 
solve it here.

Josh Luthman
24/7 Help Desk: 937-552-2340
Direct: 937-552-2343
1100 Wayne St
Suite 1337
Troy, OH 45373


On Tue, Aug 31, 2021 at 10:41 AM Mel Beckman 
<m...@beckman.org<mailto:m...@beckman.org>> wrote:
Mark,

But you said “Gas-fired furnaces or heaters should not have an impact because 
the only electrical requirement is to fire up the pilot light.” There is no 
gas-fired furnace I know of that doesn’t require a blower fan. How else does 
the heat get out of the furnace?

To answer your question, you need to understand that this safety system has two 
components. The first component, the furnace interlock relay, is designed to 
interlock the blower with the forced-air system, which also includes an outside 
air supply valve. When the blower is energized, a circuit inside the furnace 
gets power. The blower and furnace operate continuously when this circuit is 
energized, and the supply valve opens and closes as needed to ensure the air 
doesn’t get stale.

The safety second component is the limit switch, which primarily turns the 
blower fan on and off, but also has a safety role. When the temperature in the 
air supply plenum gets too hot, the limit switch turns off the furnace burner 
(or boiler, in a water-based system) to prevent damage, and possibly a fire, 
from overheating.

The actual state mechanics are thus not as simple as “if the blower fails the 
furnace won’t light”. And it’s because of these complex state mechanics that 
furnace electricity is hard wired.

Without AC power, no furnace can operate in a power outage. So that’s certainly 
not “no impact” from a utility failure. But the many thousands of deaths that 
occurred in homes and offices before these safety systems were put into the 
code is why you need a generator transfer switch if you want heat (or A/C) in 
your home during an outage.

 -mel

> On Aug 31, 2021, at 7:15 AM, Mark Tinka <mark@tinka.africa> wrote:
>
> 
>
>> On 8/31/21 16:06, Mel Beckman wrote:
>>
>> I think you’re forgetting about the all-important blower fan in a gas-fired 
>> furnace.
>
> Well, I was referring to a pure electric furnace, not one that uses a blower 
> over a gas-fired one :-).
>
> In that case, the blower is not a major draw on power.
>
> But again, we don't have those things here, so :-).
>
>
>> That said, the reason the code requires furnaces to be hardwired is to 
>> ensure that the blower interlock system can’t be bypassed. An electrical 
>> interlock ties a heat recover ventilator to circulation air blower operation 
>> of a forced-air furnace system. This ensure that the blower circulates 
>> supply and return air within the structure. A plug-in power source leads to 
>> the possibility that this interlock could be accidentally defeated, 
>> resulting in an overheat within the flame box.
>
> Makes sense.
>
> Does this, then, mean that if the blower itself were to fail, the gas burner 
> would not light?
>
> Mark.

Reply via email to