On 22 Jun 2010, at 15:54, David S. Madole wrote:

> On 6/22/2010 10:36 AM, Chris Boot wrote:
>> I just acquired a new UPS and have been trying to get it to work with NUT. 
>> It's an Eaton/Powerware 9120 700i with both USB and RS-232 interfaces.
>> 
>> So I moved on to try the serial port instead. Here the UPS also regularly 
>> loses the connection but at least it doesn't lock the UPS right up - maybe 
>> that was a fluke. If I restart the driver, the communication is regained for 
>> a few minutes but then drops again. Below are excerpts from running 
>> '/lib/nut/bcmxcp -DDD -a pw9120'.
>>   
> I had a similar problem using bcmxcp with an HP3000 XP unit.
> 
> Ultimately what fixed it was adding:
> 
>     pollinterval = 5
> 
> to the definition for the unit in ups.conf.
> 
> A value as low as 3 (compared to the default 2) seemed to be enough to fix 
> the problem, I went to 5 for some extra margin. I think that sometimes the 
> poll cycle takes more than two seconds and the next poll somehow steps on the 
> tail of the previous one. Not sure if this is the same thing you are 
> experiencing, but the symptom is the same.

Well that seems to have made it less frequent, but it still loses comms at 
least every few hours.

So where do I go from here?

Cheers,
Chris

-- 