Reading the code they removed the grid tie only and this opened the door
for off grid customers i would say its OK but i always recommend contacting
the customers tax accountant as they will sign right next to your customer
and they sometimes think different.
On Oct 29, 2014 2:13 PM, "SunHarvest"
Hi Daniel,
I typically vent them the way you do, which will allow any small
amount of hydrogen out. The customer is absolutely adamant about
venting these to the outside. I will cooperate so long as his method
doesn't compromise the system through cooling the batteries
unnecessarily in the de
HI Eric,
The DSIRE website lists the incentives, there is no requirement for grid
tie.
Have your CPA or attorney verify, you can also query the IRS.
Ag systems filing Schedule F qualify for REAP grants from the USDA.
I have done several grants and we always add the ITC and depreciation.
Eric,
My understanding is that it's a residential credit and thus has to
be used for a residence, although it's not limited to a primary
residence. So in that case, no, an irrigation pump would not be
allowed.
By the way, solar water pumping is specifically
Does anyone know for certain if a homeowner can qualify for the 30% federal
solar tax credit (ITC) if the PV is used for direct water pumping out of a well
used for irrigation? To be more specific, there are two wells that will be
solarized. One well will provide irrigation water to livestock on
All –
Just a couple of quick comments – we’ve been using both Pathfinders and
Suneye’s for several years. We’ve now primarily switched to the Solmetric
Suneye for ease of running the full analysis report. A while ago we
compared the same sites back to back between the Suneye software and
Pathfin
Hi William,
I like that idea a lot. If you went through and subtracted off the shaded
numbers for each of the Pathfinder readings on the same spreadsheet you
could get the cumulative shading for a string across those reading
locations. The Pathfinder Assistant should be able to do that, too. I lik
Hi Allen,
Thanks for the assessment. I think that makes a lot of sense. I prefer to
be conservative with my grid-tied numbers, too. Maybe I'll just round down
the Suneye projections.
Dana
Dana Brandt
Ecotech Energy Systems, LLC
www.ecotechenergy.com
d...@ecotechenergy.com
360.318.7646
On Tue, O
Hi Daniel,
You should patent that magic box idea. Better yet, patent the J-box with an
embedded addressable semiconductor switch: Permissive signal from the inverter
= switch closed; no signal from the inverter = switch open. Bob's your uncle.
Touch-safe PV modules without undue cost or complex
Thanks for the response David, this is what I was kind of expecting.
I was hoping for some sort of "magic box" that attached to the first, and
last module in the string, and would shut the string down if it lost signal
from the inverter. Similar to how solar edge works, but with only 1-2
units/
Daniel,
Here's some of what I learned about solutions for 690.12.
Residential rapid shutdown
SMA's TL-US series inverters can meet the 10 second requirement in 690.12
without further mediation. Therefore you can meet 690.12 with these string
inverters by adding a ground-level rapid shutdown co
Al,
Will you be relying on the 120% rule for your interconnection (i.e., do you
anticipate exceeding the ampacity of the conductors you’re connecting to?)? If
not, you don’t have to worry about going to the opposite end of the busbar.
If you’re on the 2014 NEC, the feeder taps rules for invert
I too saw that these were AGMS. The only time excess H venting happens is with
severe over voltage for a period of time. How often will this happen? Have any
battery wrenches experienced high volume venting of AGM’s?
Our experience: There is no NEC requirements for mobile installations. We have
I too am interested. Especially after the teaser from SMA that they would
unveil their solution to the 2014 NEC 690.12 fiasco at the show. I see
nothing on SMA's website as of yet.
With Regards,
Daniel Young,
NABCEP Certified PV Installation ProfessionalTM: Cert #031508-90
NABCEP Certified Solar
I just re-read the original post Drake. These are AGM batteries. Do you have
a "belt, suspenders,...then a rocket pack" type of client here?
We typically vent our AGM boxes with small louver vents top and bottom to
allow the batteries to ventilate for cooling purposes, not H2 concerns.
With Regar
Gentlemen & Ladies,
Anyone who went to the LAS show have any comments? Hopefully, not
everything that happens in Vegas stays in Vegas.
Thanks for sharing,
Bill Loesch
Solar 1 - Saint Louis Solar
314 631 1094
-
No virus found in this message.
Checked by AVG - www.avg.com
Version: 201
Dana,
I have never compared these two side-by-side, but I do know from experience
that it is critical to use the proper cropping margins when transferring images
in to the Pathfinder Assistant Software.
Slight changes in the margins of the field photographs of the Pathfinder tool
can have a sign
17 matches