Craig
IMHO you are up for an explosion more than a fire: you have suspended fine 
fuel, air, confinement, all you need is a spark

Suggest vyou consider spark detection as in Firefly or Grecon for activation as 
you will noty have much time to dump water or drychem on it. 

Once spark is detected dump water, gas, drycvhem as you see. Do they have 
magnetic detectors/shutdown? 
 
Sorry in a jotel room in Bangkok this is the best FM has a DS on dust system 
just don't carry the CD with me anymore.

Cheers
Jack 
Sent via BlackBerry




----- Original Message -----
From:  [EMAIL PROTECTED]
Sent: 01/17/2008 05:35 AM
To: <sprinklerforum@firesprinkler.org>
Subject: Combustible ductwork, below slab ????

THIS MESSAGE ORIGINATED ON THE INTERNET - Please read the detailed disclaimer 
below.
*****************************************************************************

We can get some odd ball stuff.

This is a materials conveying system, conveying styrofoam dust
particulate, the duct is HDPE and is buried 4-6 ft below the slab.  The
duct is 48" in Dia.  
There are 48" round manways with open grates on them every 100 ft or so.
The total length of this duct system is over 500 ft.  It picks up foam
dust from equipment as well as from the floor.

The challenge, protect this duct based on it's combustible nature and
the nature of the materials being conveyed.  Steel duct is not an option
since the duct is direct buried.

What's your approach?




Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


****************************************************************************
The following message has been automatically added by the mail gateway to 
comply with a  Royal  & 
SunAlliance IT Security requirement.

As this email arrived via the Internet you should be cautious about its origin 
and content. Replies which 
contain sensitive information or  legal/contractual obligations are 
particularly vulnerable.  In these cases 
you should not reply unless you are authorised to do so, and adequate 
encryption is employed.

If you have any questions, please speak to your local desktop support team or 
IT security contact.
****************************************************************************



**************************************************
Royal & Sun Alliance - Notice of Confidentiality

This transmission contains information that may be confidential and that
may also be privileged. Unless you are the intended recipient of the message
or authorised to receive it for the intended recipient) you may not copy,
forward, or otherwise use it, or disclose it or its contents to anyone else.
If you have received this transmission in error please notify us immediately
and delete it from your system.
**************************************************

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to