Tony,

Ask for the spec sheet and lab report on the material, the truth lies
within.  Mineral Wool, i.e. thermafiber and roxul are common non
combustible. Watch the details the code requires non combustible not
fire retardent. Cellulose Blown-In Insulation is a wood fiber based
fire-retardant but not non combustible.

Also some fiberglass insulation, i.e. no kraft facing and no plastic
reinforcement stranding is also non combustible.

Had a project a few years back that used the infill technique to avoid
suppression in concealed combustible spaces. The inspection included
selected borings through the sub floor to assure proper fill.

Hope that helps

John Drucker Jr CET
Fire Protection Subcode Official
Fire/Building/Electrical Inspector
Borough of Red Bank, NJ 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of A.P.Silva
Sent: Wednesday, April 21, 2010 1:11 PM
To: [email protected]
Subject: Cellulose Fibre Insulation

 
I have a 14" deep open web wood truss floor space filled with "blown
Cellufibre sound attenuation insulation". Anyone know whether this
insulation is "non-combustible" complying with a combustible concealed
space permitted by NFPA to be unsprinklered? They claim the insulation
is fire retardant. But I'm not sure. 

Tony  

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)


CONFIDENTIAL AND PROPRIETARY:
This email message is intended only for the use of the individual or entity to 
which it is addressed and may contain information that is privileged and 
confidential, nor is it, unless specifically stated, intended to be relied upon 
by any person or persons other than the individual or entity named above and no 
warranties or representations are made or intended to persons or entities not 
named above.  If the reader is not the intended recipient, you are hereby 
notified that any dissemination, distribution or copying of this communication 
is strictly prohibited.  If you have received this communication in error, 
please notify us immediately by telephone, return this message to the address 
above and delete all copies.  Thank you.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to