NFPA 72 requires 90 seconds. 

Forest Wilson
Cherokee Fire

Sent from my Verizon Wireless Phone

----- Reply message -----
From: "Gregg Fontes" <[email protected]>
Date: Mon, Aug 23, 2010 12:40 pm
Subject: Audible Water Flow Time
To: <[email protected]>

If not mistaken, NFPA 13 allows up to 5 minutes to receive an audible alarm
through the inspectors test on a wet pipe system.  On a standard wet pipe
system, was there or is there any other requirement that would limit the
audible alarm to 60 seconds?

Thanks,
Gregg Fontes
Cen-Cal Fire Systems, Inc.