The requirement for an audible waterflow alarm signal under NFPA 13-2007 is
not more than 5 minutes under 6.9.1 (this is the non-silenceable water gong
connection in the alarm valve trim)

The requirement for a waterflow alarm when the sprinkler is supervised with
a fire alarm under NFPA 72-2007 Section is 5.11.2 and that is a maximum of
90 seconds delay after sustained flow begins.

Depending on the local building code in effect a sprinkler system may not
necessarily require a connection to a supervisory control unit and can just
be required to have the exterior audible waterflow gong / bell / horn in
which case the requirements of NFPA 13 are applied solely.

If there is a building wide fire alarm system installed or the sprinkler
system is supervised through a control unit and possibly a supervising
station then the requirements of NFPA 72 are applied, but that does not
necessarily negate the dedicate waterflow gong / bell / horn.  The IBC
actually requires the local alarm and mandates the connection to the
building wide alarm where such exists.

Generally a mix of line voltage electric bell or water motor gong on one
pair of flowswitch contacts and the low voltage 12/24 volt alarm IDC/SLC on
the other pair of contacts to make code compliance.  Hence the major
manufacturer's make their flow switch with two sets of isolated contacts and
a divided compartment to also be compliant with the NEC.

Did that answer it or was there another issue?

Dave P.



------------------------------

Message: 14
Date: Mon, 23 Aug 2010 09:40:37 -0700
From: "Gregg Fontes" <[email protected]>
To: <[email protected]>
Subject: Audible Water Flow Time
Message-ID: <[email protected]>
Content-Type: text/plain;       charset="us-ascii"

If not mistaken, NFPA 13 allows up to 5 minutes to receive an audible alarm
through the inspectors test on a wet pipe system.  On a standard wet pipe
system, was there or is there any other requirement that would limit the
audible alarm to 60 seconds?

Thanks,
Gregg Fontes
Cen-Cal Fire Systems, Inc.
209-334-9119

**********************************************


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to