Just got into the office, Left Coast Style.   I don't know where to
begin on this one - you apparently have a set of construction documents
that include an FPE or ME's take on the basis of design for fire
sprinklers?   And they specify 13D and then map the compartments into
hazard groups?   What hazard did the classify the fire pump room?  Is it
2-hr. construction?   Sorry, no more sarcasm.  

IMHO a halfway house (i.e. group home) should be a 13R, not a 13D
design.  13R addresses areas outside the dwelling units and defers to 13
for hazard groups, so the EOR's basis of design MAY be sort of on the
right track but his or her choice of the applicable standard is not
congruent.   Also, I recommend that you forget about "density" when
applying residential sprinklers per 13D and 13R; instead, refer to the
manufacturer's data sheets as many (most?)) residential sprinklers have
minimum flows that exceed .05 density, especially sidewalls and sloped
ceiling applications.   

I don't believe you've lost your mind, but if you stay in this business
you most certainly will.   To maintain sanity and gain perspective on
how to deal with projects like this, I recommend you read a book called
"A Confederacy of Dunces."  The foregoing is my opinion only and does
not necessarily represent the opinion or intent of the NFPA 13D/13R
Technical Committee on Residential Sprinkler Systems, nor is it intended
to psychologically profile Architects, Fire Protection Engineers, etc.

Steve Leyton
Protection Design & Consulting
San Diego, CA


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Brian
Harris
Sent: Wednesday, September 19, 2012 7:14 AM
To: [email protected]
Subject: Re: Residential Question

It's being used as a halfway house, the specs and drawings call it out
as a 13D system, attic and crawl spaces not sprinkled etc.

Sent From My iPhone..

On Sep 19, 2012, at 9:57 AM, "IPA" <[email protected]> wrote:

> If it's truly a 13d system it is a min of .05 density throughout - 
> there are no light or ordinary hazard areas. Is it possible that this 
> 'house' is being used for something other than single family living 
> such as a nursery home, school, or something else requiring additional
sprinkler protection?
> Just because something looks like a house doesn't mean it's going to 
> be used as one. Otherwise sounds like it could just be a confused
architect.
>
>
>
> On Wed, Sep 19, 2012 at 6:08 AM, Brian Harris
<[email protected]>wrote:
>
>> I admit I don't do many residential systems so this questions might 
>> seem strange but I have a 13D system and there are notes on the FP 
>> drawings that are calling some areas Light Hazard & some Ordinary 
>> Hazard & then list the densities accordingly. Here's where the 
>> confusion comes in, if it's a 13D system would I design the whole 
>> thing to 0.05/sq.ft ? The residential heads spec'd out are all
figured that way as well. Have I totally lost my mind?
>>
>> Brian Harris, CET
>> BVS Systems Inc.
>> Sprinkler Division
>> bvssystemsinc.com<http://bvssystemsinc.com/>
>> Phone: 704.896.9989
>> Fax: 704.896.1935
>>
>> -------------- next part -------------- An HTML attachment was 
>> scrubbed...
>> URL: <
>> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/atta
>> chments/20120919/e26771ac/attachment.html
>>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
> -------------- next part -------------- An HTML attachment was 
> scrubbed...
> URL: 
> <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/atta
> chments/20120919/2d2d2c82/attachment.html>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to