Don' t over look the other possibilities

1. The FPE/ME sat down long and hard and really meant exactly what was produced 
in the construction documents based on their judgment?  It's a 13D with some 
modifications as shown?  
2. The design team and AHJ traded other perhaps totally non-fire related issues 
for a different sprinkler design? 

And whether Steve's scenario is correct or the above is correct none of it 
really matters if you already signed the contract.  You are looking at 
installing 13D with modified densities.  Certainly odd doesn't violate code. 
Supporting background isn't necessary on the drawings. 

For the record I'd bet with Steve on this one.  Just don't go flying off the 
handle and later find the above and you are held to the contract you signed and 
if you walk away the CG pulls your bond.....and the bond company comes and 
takes your first born and sends you the bill on top of that.  

Chris Cahill, PE*
Senior Fire Protection Engineer, Aviation & Facilities Group
Burns & McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com

Proud to be one of FORTUNE's 100 Best Companies to Work For
*Registered in: MN





-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Steve Leyton
Sent: Wednesday, September 19, 2012 10:05 AM
To: [email protected]
Subject: RE: Residential Question

Just got into the office, Left Coast Style.   I don't know where to
begin on this one - you apparently have a set of construction documents that 
include an FPE or ME's take on the basis of design for fire
sprinklers?   And they specify 13D and then map the compartments into
hazard groups?   What hazard did the classify the fire pump room?  Is it
2-hr. construction?   Sorry, no more sarcasm.  

IMHO a halfway house (i.e. group home) should be a 13R, not a 13D design.  13R 
addresses areas outside the dwelling units and defers to 13 for hazard groups, 
so the EOR's basis of design MAY be sort of on the right track but his or her 
choice of the applicable standard is not
congruent.   Also, I recommend that you forget about "density" when
applying residential sprinklers per 13D and 13R; instead, refer to the 
manufacturer's data sheets as many (most?)) residential sprinklers have minimum 
flows that exceed .05 density, especially sidewalls and sloped
ceiling applications.   

I don't believe you've lost your mind, but if you stay in this business
you most certainly will.   To maintain sanity and gain perspective on
how to deal with projects like this, I recommend you read a book called "A 
Confederacy of Dunces."  The foregoing is my opinion only and does not 
necessarily represent the opinion or intent of the NFPA 13D/13R Technical 
Committee on Residential Sprinkler Systems, nor is it intended to 
psychologically profile Architects, Fire Protection Engineers, etc.

Steve Leyton
Protection Design & Consulting
San Diego, CA


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Brian Harris
Sent: Wednesday, September 19, 2012 7:14 AM
To: [email protected]
Subject: Re: Residential Question

It's being used as a halfway house, the specs and drawings call it out as a 13D 
system, attic and crawl spaces not sprinkled etc.

Sent From My iPhone..

On Sep 19, 2012, at 9:57 AM, "IPA" <[email protected]> wrote:

> If it's truly a 13d system it is a min of .05 density throughout - 
> there are no light or ordinary hazard areas. Is it possible that this 
> 'house' is being used for something other than single family living 
> such as a nursery home, school, or something else requiring additional
sprinkler protection?
> Just because something looks like a house doesn't mean it's going to 
> be used as one. Otherwise sounds like it could just be a confused
architect.
>
>
>
> On Wed, Sep 19, 2012 at 6:08 AM, Brian Harris
<[email protected]>wrote:
>
>> I admit I don't do many residential systems so this questions might 
>> seem strange but I have a 13D system and there are notes on the FP 
>> drawings that are calling some areas Light Hazard & some Ordinary 
>> Hazard & then list the densities accordingly. Here's where the 
>> confusion comes in, if it's a 13D system would I design the whole 
>> thing to 0.05/sq.ft ? The residential heads spec'd out are all
figured that way as well. Have I totally lost my mind?
>>
>> Brian Harris, CET
>> BVS Systems Inc.
>> Sprinkler Division
>> bvssystemsinc.com<http://bvssystemsinc.com/>
>> Phone: 704.896.9989
>> Fax: 704.896.1935
>>
>> -------------- next part -------------- An HTML attachment was 
>> scrubbed...
>> URL: <
>> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/atta
>> chments/20120919/e26771ac/attachment.html
>>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
> -------------- next part -------------- An HTML attachment was 
> scrubbed...
> URL: 
> <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/atta
> chments/20120919/2d2d2c82/attachment.html>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to