A fire official here in SoCal asked me to forward his comments on
current topics, as he's having a problem getting his replies to post to
the forum:    

 

*       According to 2010 California Building Code Section 310 halfway
houses are classified as either Group R-2.1 or Group R-4 occupancies
depending on the ambulatory status of the clients. Referring then to
Section 903.2.8 it specifically prohibits a 13D system in Group R-2.1 &
R-4 occupancies. Halfway houses must utilize a full 13 system. 

 

*       Basement Storage in Multi-Residential: According to the Building
Code the common storage area located in the basement of a Group R-2
multi-residential building such as apartments or condos would be a Group
S-1 occupancy which must be separated from the R-2 by one-hour fire
barriers. While the R-2 may be protected by a 13R system, the S-1 must
be protected by a full 13 system. 

 

Galen Taylor

Fire Prevention Engineering Assistant

County of Los Angeles Fire Department

Fire Prevention Engineering - Special Projects