I see an Exception from the area requirements of Table 910.3 but there is no
exception from the need to separate ESFR from conventional.  So when there
is a need for a draft curtain there would be a minimum 4 ft depth.  Perhaps
someone can help me with this.  I am not involved with storage 24/7.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bobby Gillett
Sent: Thursday, September 20, 2012 1:14 PM
To: [email protected]
Subject: RE: Draft curtain

Thank you both. I did mean IFC Bill - thank you. The only reason for the
draft curtain is due to the different response elements of the sprinklers as
Chris said. Looking at IFC 2006 910.3.5 it appears my situation qualifies
for the "Exception" and I can apply the 2'-0 depth as referenced in NFPA13
2007 8.4.6.4. It will be smoke tight.

Thanks again. 

Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office  (731) 424-9285 fax
(731) 267-4853 cell
www.keyfireprotection.com
 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bill Brooks
Sent: Thursday, September 20, 2012 12:06 PM
To: [email protected]
Subject: RE: Draft curtain

Table 910.3 and Section 910.3.5 of the 2006 International FIRE Code if this
is adopted.  It notes the ESFR to non-ESFR boundary.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bobby Gillett
Sent: Thursday, September 20, 2012 12:56 PM
To: [email protected]
Subject: RE: Draft curtain

Thank you - 2006 IBC - do you know the label of the section its in - I
glanced and didn't see it.

Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office  (731) 424-9285 fax
(731) 267-4853 cell
www.keyfireprotection.com
 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bill Brooks
Sent: Thursday, September 20, 2012 11:48 AM
To: [email protected]
Subject: RE: Draft curtain

See 2009 International Fire Code for some guidelines/requirements before you
confirm the depth of the curtain or the construction. Just using this
reference as an example since you didn't specify the applicable code in this
jurisdiction.  I don't think the cover on both sides is necessary.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Byron Weisz -
Cen-Cal Fire Systems
Sent: Thursday, September 20, 2012 12:22 PM
To: [email protected]
Subject: RE: Draft curtain

That is a Building Code issue

Byron Weisz
 
Cen-Cal Fire Systems, Inc.
1615 So. Stockton St. 
Lodi, CA. 95240
Ph.   (209) 334-9119
Fax   (209) 334-2923
[email protected]
 
This message is intended only for the use of the individual or entity to
which it is addressed and may contain information that is privileged and/or
confidential. If you are not the intended recipient any use, dissemination,
distribution, or copying of this communication and attachments is strictly
prohibited. Thank you.
 
 
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bobby Gillett
Sent: Thursday, September 20, 2012 8:50 AM
To: [email protected]
Subject: Draft curtain
Importance: High

We have a project that we are demo'ing a pipe schedule system and installing
a ESFR system for storage. There is an adjacent area of the building that
will have a pipe schedule system w/standard response sprinklers in it. Per
NFPA13 2007 8.4.6.4 the owner will provide a draft curtain since a wall is
out of the question in this area. The draft curtain will be 2'-0 down from
the deck constructed of non-combustible materials and sealed at the deck
(probably smoke caulk). The owner is going to provide a 4'-0 clear aisle
centered on the curtain (2'-0 each way). The contractor plans on using metal
studs and roof decking material for the curtain. The question is, do the
studs have to be covered each side or is putting the decking on one side
sufficient? I didn't see anything as far as thickness of curtain or that
would lead me to believe it would have to be covered each side. 

 

Thank you,

 

Bobby Gillett

Sr. Project Manager

Key Fire Protection, Inc.

(731) 424-0130 office  (731) 424-9285 fax 

(731) 267-4853 cell

 <http://www.keyfireprotection.com> www.keyfireprotection.com

 

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20120920/20d1b142/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2012.0.2221 / Virus Database: 2441/5281 - Release Date: 09/20/12

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2012.0.2221 / Virus Database: 2441/5281 - Release Date: 09/20/12

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to