I agree there is some confusion in 910 when not required to have smoke and heat 
venting and draft curtains because of the 'otherwise installed' in 901.1.   I 
don't know if I have the definitive answer because the more I read it the more 
confused I get.  We're otherwise installing them due to 13.  So once we do that 
IFC 910 kicks in?

Here's another twist.  910.2 is where required and it only requires smoke and 
heat venting in certain cases, 50,000 sq.ft. F-1 and S-1 and HPS.   901.3 is 
the design and installation of vents and curtains, NOT where required.  One 
could argue DC's are never required by the IFC because if they were it should 
be in the where required section of 910.2.  

Moving back to the otherwise installed of 910.1 the how to design section 
certainly seems to say 4' minimum.  I'd counter the more specific requirement 
of NFPA 13 takes precedence.  Yes, I know Codes trump Standards.  But this is 
not a case of Codes requires one thing and Standard requires another.  The 
curtains are for different purposes.  IFC has draft curtains for control smoke, 
NFPA 13 is to prevent the wrong heads from operating.  

I also defer to the NFPA committees over ICC committees as NFPA are specialists 
in the subject at hand.  ICC covers a lot more ground and are thus more 
generalists.  In-other-words do you put your faith in someone that is 
interested in sprinklers (NFPA 13) or fire code administration, fire truck 
access, emergency planning, egress, fire alarm, fire suppression, fire 
sprinklers, aviation, dry cleaning, lumber yards, hazardous materials ........ 
the sprinkler guys say 2' is good enough the generalists wrote a confusing 
section.  I'm certainly not bashing ICC I just don't believe anyone can be that 
good in EVERYTHING. 

I'll also admit a bias against smoke and heat venting and curtains as they have 
been shown to fail sprinklers in some cases.  Or at least a bias in these 
industrial type occupancies vs. highrises and atriums.  If the sprinklers work 
there is a lot of cold smoke and vents and curtains provide marginal benefit.   
If the sprinklers don't work there will shortly be a vent right near the fire, 
lol.   

Chris Cahill, PE*
Senior Fire Protection Engineer, Aviation & Facilities Group
Burns & McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com

Proud to be one of FORTUNE's 100 Best Companies to Work For
*Registered in: MN





-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Bill Brooks
Sent: Thursday, September 20, 2012 12:33 PM
To: [email protected]
Subject: RE: Draft curtain

I see an Exception from the area requirements of Table 910.3 but there is no 
exception from the need to separate ESFR from conventional.  So when there is a 
need for a draft curtain there would be a minimum 4 ft depth.  Perhaps someone 
can help me with this.  I am not involved with storage 24/7.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bobby Gillett
Sent: Thursday, September 20, 2012 1:14 PM
To: [email protected]
Subject: RE: Draft curtain

Thank you both. I did mean IFC Bill - thank you. The only reason for the draft 
curtain is due to the different response elements of the sprinklers as Chris 
said. Looking at IFC 2006 910.3.5 it appears my situation qualifies for the 
"Exception" and I can apply the 2'-0 depth as referenced in NFPA13
2007 8.4.6.4. It will be smoke tight.

Thanks again. 

Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office  (731) 424-9285 fax
(731) 267-4853 cell
www.keyfireprotection.com
 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bill Brooks
Sent: Thursday, September 20, 2012 12:06 PM
To: [email protected]
Subject: RE: Draft curtain

Table 910.3 and Section 910.3.5 of the 2006 International FIRE Code if this is 
adopted.  It notes the ESFR to non-ESFR boundary.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bobby Gillett
Sent: Thursday, September 20, 2012 12:56 PM
To: [email protected]
Subject: RE: Draft curtain

Thank you - 2006 IBC - do you know the label of the section its in - I glanced 
and didn't see it.

Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office  (731) 424-9285 fax
(731) 267-4853 cell
www.keyfireprotection.com
 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bill Brooks
Sent: Thursday, September 20, 2012 11:48 AM
To: [email protected]
Subject: RE: Draft curtain

See 2009 International Fire Code for some guidelines/requirements before you 
confirm the depth of the curtain or the construction. Just using this reference 
as an example since you didn't specify the applicable code in this 
jurisdiction.  I don't think the cover on both sides is necessary.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Byron Weisz - 
Cen-Cal Fire Systems
Sent: Thursday, September 20, 2012 12:22 PM
To: [email protected]
Subject: RE: Draft curtain

That is a Building Code issue

Byron Weisz
 
Cen-Cal Fire Systems, Inc.
1615 So. Stockton St. 
Lodi, CA. 95240
Ph.   (209) 334-9119
Fax   (209) 334-2923
[email protected]
 
This message is intended only for the use of the individual or entity to which 
it is addressed and may contain information that is privileged and/or 
confidential. If you are not the intended recipient any use, dissemination, 
distribution, or copying of this communication and attachments is strictly 
prohibited. Thank you.
 
 
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bobby Gillett
Sent: Thursday, September 20, 2012 8:50 AM
To: [email protected]
Subject: Draft curtain
Importance: High

We have a project that we are demo'ing a pipe schedule system and installing a 
ESFR system for storage. There is an adjacent area of the building that will 
have a pipe schedule system w/standard response sprinklers in it. Per
NFPA13 2007 8.4.6.4 the owner will provide a draft curtain since a wall is out 
of the question in this area. The draft curtain will be 2'-0 down from the deck 
constructed of non-combustible materials and sealed at the deck (probably smoke 
caulk). The owner is going to provide a 4'-0 clear aisle centered on the 
curtain (2'-0 each way). The contractor plans on using metal studs and roof 
decking material for the curtain. The question is, do the studs have to be 
covered each side or is putting the decking on one side sufficient? I didn't 
see anything as far as thickness of curtain or that would lead me to believe it 
would have to be covered each side. 

 

Thank you,

 

Bobby Gillett

Sr. Project Manager

Key Fire Protection, Inc.

(731) 424-0130 office  (731) 424-9285 fax 

(731) 267-4853 cell

 <http://www.keyfireprotection.com> www.keyfireprotection.com

 

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20120920/20d1b142/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2012.0.2221 / Virus Database: 2441/5281 - Release Date: 09/20/12

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2012.0.2221 / Virus Database: 2441/5281 - Release Date: 09/20/12

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to