Not to prolong the prolongation but ...   

Galen's comments were based in part on CA amendments, so like much of
what we discuss here in the forum, there isn't necessarily one global
solution.   I'm not sure as to what other states may do, but generally
the applicability of 13R is governed by construction type and whether or
not the sprinklers are counted as a substitution or not.  Once common
miss is that 13R systems are used (or proposed) in buildings taking an
additional story and the building code says you can't do that, it must
be 13.   As to the specifics of the thread, you are - of course -
technically correct in that you pick a design basis and stay with it.
But in the case of this basement I'm still not understanding of the
compartmentalization or reduction in density issues that have been
raised.  Whether the BOD is 13R or 13 is irrelevant: it's an area
outside the dwelling unit, it's not misc. storage (an accessory use)
it's GENERAL storage (a dedicated use) and every way I look at it the
design comes back to OH2 per NFPA 13. 

The foregoing is my opinion only and does not necessarily represent the
opinion or intent of the NFPA 13D/13R Technical Committee on Residential
Sprinkler Systems.

Steve Leyton
Protection Design & Consulting
San Diego, CA


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Mark
Sornsin
Sent: Thursday, September 20, 2012 10:53 AM
To: [email protected]
Subject: RE: Excellent comments from a smart guy

Not to prolong this discussion, but... 

" Basement Storage in Multi-Residential: According to the Building ode
the common storage area located in the basement of a Group R-2
multi-residential building such as apartments or condos would be a Group
-1 occupancy which must be separated from the R-2 by one-hour fire
barriers. While the R-2 may be protected by a 13R system, the S-1 must e
protected by a full 13 system. "

Isn't it more accurate to say that given the S-1 occupancy in the
basement, and R-2 on the floors above, the system is to be designed to
NFPA 13R, with the storage areas getting their protection criteria from
NFPA 13? The point being: you don't design a building to both NFPA 13
and 13R. It sounds like semantics, but it more than that because being
part of a larger NFPA 13R building, that storage area does NOT
necessitate all of the design requirements of NFPA 13.

Mark A. Sornsin, PE| Fire Protection Engineer Ulteig Engineers, Inc.|
Fargo, ND [email protected]
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to