I'm also in a jurisdiction where an addendum to the building code requires
sprinklers in balconies and patios of 13R buildings if the buildings are of
combustible construction. They are required with or without overhangs. I
think the approach should be to provide sprinklers outside for exposure
protection where radiation is the critical mode of heat transmission. So
overhangs need not be provided. My only concern is heads need to be
protected from hail, which is also a problem in this area.

Tony   

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Todd Williams
Sent: October 8, 2012 5:50 AM
To: [email protected]
Subject: 13R balcony protection

The Connecticut Fire Safety Code (at least the part that is based on the
IFC) includes a requirement that exterior balconies and patios be
sprinkelred in 13R occupancies. However, this is being interpreted that they
have to be protected regardless if there is any structure above or not.
Consequently, we have to install sidewall sprinklers under 9" door moldings
because they open on to a patio or deck (just got a plan rejected for this).
This make no sense to me because they would most likely never activate, but
this is being enforced as the law. Anybody else run into this?

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to