I knew I was asking for trouble, even with the semi-quotes 'full scale'. The
key is "more satisfying". If I say 20 heads at .2/X sq ft will control a Y
size fire..., just flowing 20 heads to verify the calcs, even with-out a
fire might be destructive. But if I say it will take (4) 40,000 CFM fans to
keep conditions tenable @ 6 feet above the highest level of egress, at least
I get to see all the fans 'flowing'. With both the suppression and the
tenability, the FULL SCALE destructive tests have already been done.

-----Original Message-----
From: Cahill, Christopher [mailto:[email protected]] 
Sent: Monday, October 15, 2012 9:16 AM
To: [email protected]
Subject: RE: 13R balcony protection

"smoke control systems can be tested 'full scale' and not be destructive
doing so."  How do you do that?  If you are not testing with hot or at least
a very buoyant 'smoke' plume you probably aren't really testing it.    

Chris Cahill, PE*
Senior Fire Protection Engineer, Aviation & Facilities Group
Burns & McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com

Proud to be one of FORTUNE's 100 Best Companies to Work For
*Registered in: MN





-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Brad
Casterline
Sent: Monday, October 15, 2012 9:07 AM
To: [email protected]
Subject: RE: 13R balcony protection

Agree George-- I do not see how it could be otherwise. Expert witnesses for
the prosecution and the defense both can "prove" whatever they want to using
modeling :(. I use it to get a second opinion of what my gut is telling me,
and for something enjoyable and fascinating to do home nights and weekends.
I have used FDS far more for designing smoke exhaust and EVAC, than
sprinkler models- also fascinating (to me) and more satisfying in that smoke
control systems can be tested 'full scale' and not be destructive doing so. 

-----Original Message-----
From: George Church [mailto:[email protected]]
Sent: Monday, October 15, 2012 7:46 AM
To: [email protected]
Subject: RE: 13R balcony protection

I suppose it's just since we apply the codes and standards as adopted so
most AHJs don't know and don't care if we can model something or draw other
conclusions than what they're reading in black and white, day in and day
out.


George L.  Church, Jr., CET
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
[email protected]


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to