In a jurisdiction near Bruce there was one 

Ron Greenman 
...On the phone

On Oct 15, 2012, at 12:49 PM, "Bruce Verhei"<[email protected]> wrote:

> The jurisdiction I worked for has had a whole series of these fires. Fire 
> burns up till attic is reached, and attic is burned off. On occupied floors 
> windows break out and fire bursts into living areas.  Heads operate on each 
> floor. We've only had three floor structures, not four, with this scenario 
> (at least sprinklered). 10-22 heads total operate. Fire is controlled in the 
> living areas. This includes systems installed back with the old PB heat fused 
> systems, as well as listed CPVC.
> 
> Structures stripped down to the framing, new roof trusses, some ceilings 
> joists removed and replaced, or sistered in, building dried in, structural 
> members  dehydrated for awhile, then units rebuilt, has been typical. Oh, 
> first electrical and sprinklers isolated so adjacent stacks can be occupied.
> 
> Bv
> 
> 
> Sent from my Motorola ATRIX™ 4G on AT&T
> 
> -----Original message-----
> From: Tom Duross <[email protected]>
> To: [email protected]
> Sent: Mon, Oct 15, 2012 22:28:04 GMT+00:00
> Subject: RE: 13R balcony protection
> 
> 10-12 years back, apt complex called the Rosecliff 1/2 mile south down
> Willard Street from NFPA.  BBQ on 2nd level (called a Balcony in the news),
> up the exterior and into the unsprinklered attic (13R).  Nobody died
> thankfully.
> I've had Owners argue that the plan says 'deck', so why do I need to
> sprinkler?
> Wishing I was in HI...
> TD
> 
> 
> Chris, in Eastern CT, we had 2 fires (in the same city) where unprotected
> porches added significantly to the extent of fire damage. That was one of
> the deciding factors here.
> 
> 
> At 08:53 AM 10/15/2012, you wrote:
>> Curious on the addition of balconies.  It has been that way (without
> balconies) in 13R for 20 years...what caused the change now?
>> 
>> 
>> The 2009 edition of the IBC added the balcony must have a roof or deck 
>> above regarding required sprinkler protection.  Nothing regarding 
>> whether the overhang on the top floor is a driver.  Additionally, the
>> 2013 edition of NFOA 13R finally acknowledge the supremacy of the code over
> standards in driving such matters and added the below text.
>> 
>> 
>> 6.6.5* Except as provided for in 6.6.5.1, sprinklers shall not be required
> in any porches, balconies, corridors, carports, porte cocheres, and stairs
> that are open and attached.
>> 
>> 6.6.5.1 Where a roof or deck is provided above, sprinklers shall be
> installed to protect attached exterior balconies, attached exterior decks,
> and ground floor patios serving dwelling units in buildings of Construction
> Type V.
>> 
>> 6.6.5.1.1 Where sidewall sprinklers are installed beneath decks or
> balconies constructed with open wood joists, sprinklers shall be permitted
> to be installed with deflectors not less than 1 in. (25 mm) or more than 6
> in. (152 mm) below the structural members, provided that the deflector is
> not more than 14 in. (356 mm) below the underside surface of the deck.
> systems, or other reliable means capable of maintaining a minimum
> temperature between 40°F and 120°F (4°C and 48.9°C).
>> 
>> Roland
>> 
>> 
>> 
>> 
>> On Oct 8, 2012, at 4:50 AM, Todd Williams wrote:
>> 
>>> The Connecticut Fire Safety Code (at least the part that is based on 
>>> the IFC) includes a requirement that exterior balconies and patios be 
>>> sprinkelred in 13R occupancies. However, this is being interpreted 
>>> that they have to be protected regardless if there is any structure 
>>> above or not. Consequently, we have to install sidewall sprinklers 
>>> under 9" door moldings because they open on to a patio or deck (just 
>>> got a plan rejected for this). This make no sense to me because they 
>>> would most likely never activate, but this is being enforced as the 
>>> law. Anybody else run into this?
>>> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL: 
> <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20121015/46a273e2/attachment.html>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to