Are the two checks with with small holes present in the sensing lines, might 
solve your problem. See NFPA 20 for suggested arrangement

Regards,
Jamey

On 2012-11-06, at 2:52 PM, Mike Hairfield <[email protected]> wrote:

> 
> 
> I have a dry system fed by a booster pump that takes suction off of a pumped 
> well system
> feeding a plant.
> 
> The darn dry pipe valve keeps tripping and my thoughts are that when the 
> plant well pumps
> shut off it's sending a water hammer into the fire pump suction line.
> 
> I believe the water hammer is causing the pump sensing line to act erratic 
> causing the pump to run thus
> tripping the dry pipe valve.
> 
> Anyone have any suggestions about how to fix my problem, a expansion tank or 
> water hammer arrestor
> comes to mind.
> 
> Thanks,
> 
> Mike Hairfield
> 
>                           