That's only part of it:  you size the tank for the greater of
(sprinklers + HSA) or the fire flow demand, whichever is greater when
calculated as flow x duration. 

Steve L.




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
Jack Carlson
Sent: Monday, May 13, 2013 10:31 AM
To: [email protected]
Subject: RE: Sizing tanks with hydrants?


Yes - Tank serves sprinklers and hydrants

NFPA 13 2010 edition

Figure 11.2.3.1.1       .20/1500

Table 11.2.3.1.2                250 hose for 60 minutes min (assume
remote supervision)


Jack W. Carlson, SET
Triple "A" Fire Protection
Office - 251.649.2034
Fax - 251.649.2037
Cell - 706.247.5050

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
Bobby Gillett
Sent: Monday, May 13, 2013 1:19 PM
To: [email protected]
Subject: Sizing tanks with hydrants?

When sizing a water storage tank feeding a fire pump for a new facility
with multiple sprinkler systems and fire hydrants, do you have to
include any type of allowance for the hydrants? The tank will be the
sole source of supply for all (rural area). There will be no hose
stations or standpipes, only interior sprinkler systems - OH Group II
with monitored alarms.
Typically this would be an 18,000 gallon tank minimum (.20x1500x60
mins). I don't see anywhere that requires this, just making sure.

 

Thank you in advance.

 

Bobby Gillett

Sr. Project Manager

Key Fire Protection, Inc.

(731) 424-0130 office  (731) 424-9285 fax 

(731) 267-4853 cell

 <http://www.keyfireprotection.com> www.keyfireprotection.com

 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to