Usually.  The only real-world exception that comes to mind would be if
you a relatively small building of fire resistive construction and a
very demanding sprinkler system such as for H-occupancies or really
demanding storage.   I could see a situation where you had a
2,000gpm-or-less fire flow (at 20psi) and a +2000gpm CMSA including
500gpm hose, but it would be a pretty weird-looking or very hazardously
loaded building.  

Steve 




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ron
Greenman
Sent: Monday, May 13, 2013 10:37 AM
To: [email protected]
Subject: Re: Sizing tanks with hydrants?

Won't fire flow always exceed sprinkies and hose allowance?


On Mon, May 13, 2013 at 10:35 AM, Steve Leyton
<[email protected]>wrote:

> That's only part of it:  you size the tank for the greater of 
> (sprinklers + HSA) or the fire flow demand, whichever is greater when 
> calculated as flow x duration.
>
> Steve L.
>
>
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of 
> Jack Carlson
> Sent: Monday, May 13, 2013 10:31 AM
> To: [email protected]
> Subject: RE: Sizing tanks with hydrants?
>
>
> Yes - Tank serves sprinklers and hydrants
>
> NFPA 13 2010 edition
>
> Figure 11.2.3.1.1       .20/1500
>
> Table 11.2.3.1.2                250 hose for 60 minutes min (assume
> remote supervision)
>
>
> Jack W. Carlson, SET
> Triple "A" Fire Protection
> Office - 251.649.2034
> Fax - 251.649.2037
> Cell - 706.247.5050
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of 
> Bobby Gillett
> Sent: Monday, May 13, 2013 1:19 PM
> To: [email protected]
> Subject: Sizing tanks with hydrants?
>
> When sizing a water storage tank feeding a fire pump for a new 
> facility with multiple sprinkler systems and fire hydrants, do you 
> have to include any type of allowance for the hydrants? The tank will 
> be the sole source of supply for all (rural area). There will be no 
> hose stations or standpipes, only interior sprinkler systems - OH 
> Group II with monitored alarms.
> Typically this would be an 18,000 gallon tank minimum (.20x1500x60 
> mins). I don't see anywhere that requires this, just making sure.
>
>
>
> Thank you in advance.
>
>
>
> Bobby Gillett
>
> Sr. Project Manager
>
> Key Fire Protection, Inc.
>
> (731) 424-0130 office  (731) 424-9285 fax
>
> (731) 267-4853 cell
>
>  <http://www.keyfireprotection.com> www.keyfireprotection.com
>
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er
> .org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er
> .org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>



--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis
Bacon, essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to