Hmmm...back to the fire code and building code first.  Is it required to be 
sprinklered?  Has the architect taken any advantages to area, height, 
separation, etc., based upon sprinklers?  If so, gas or dry chem. don't 
substitute for required sprinklers...

Scott
 
(763) 425-1001 Office
(612) 759-5556 Cell


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Monday, May 13, 2013 1:17 PM
To: [email protected]; [email protected]
Subject: RE: Extra Hazard storage

Is it bigger than a breadbox?   

Dry chem. Is typically reserved for protecting areas inside equipment.  Not 
occupied or potentially occupied spaces.  

For large areas there are so many problems with keeping the area tight to 
contain gas such as FM-200 that it would be virtually impossible. Also gas 
systems aren't going to suitable for every commodity.  And lastly, if the Codes 
require sprinkler protection, most AHJ's aren't going to go along with a gas 
only system as primary. 

So the questions arises as to why do you want to use gas instead of sprinklers? 

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Craig 
Leadbetter
Sent: Monday, May 13, 2013 1:56 PM
To: [email protected]
Subject: Extra Hazard storage

Can an extra hazard storage facility be protected by a gas system or dry 
chemical system?



--
Craig Leadbetter
Safeguard of Marquette
PO Box 116
Marquette, MI 49855

(O) 906-475-9955
(F) 906-475-5474
(C) 906-362-5393

[email protected]
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to