Scott, Unfortunately this is a design build project government project and the whole spec is about 60 pages and the fire protection spec is limited in the requirements except to meet code, although they did mention the classification of the storage and the 13 gpm well that is on site for our use for the fire protection system. the building is unheated so i am not sure the other solutions would work.
Based on NFPA 30 and the classification of the building it would be required to be sprinklered. I am just for looking for alternatives for the design build contractor. If there are no suitable alternatives then a 200,000 (plus) gallon tank will have to be installed. The entire building is only 2,400 sqft. It will another good use of our tax dollars. On Mon, May 13, 2013 at 2:43 PM, Scott A Futrell <[email protected]> wrote: > Hmmm...back to the fire code and building code first. Is it required to > be sprinklered? Has the architect taken any advantages to area, height, > separation, etc., based upon sprinklers? If so, gas or dry chem. don't > substitute for required sprinklers... > > Scott > > (763) 425-1001 Office > (612) 759-5556 Cell > > > -----Original Message----- > From: [email protected] [mailto: > [email protected]] On Behalf Of > [email protected] > Sent: Monday, May 13, 2013 1:17 PM > To: [email protected]; > [email protected] > Subject: RE: Extra Hazard storage > > Is it bigger than a breadbox? > > Dry chem. Is typically reserved for protecting areas inside equipment. > Not occupied or potentially occupied spaces. > > For large areas there are so many problems with keeping the area tight to > contain gas such as FM-200 that it would be virtually impossible. Also gas > systems aren't going to suitable for every commodity. And lastly, if the > Codes require sprinkler protection, most AHJ's aren't going to go along > with a gas only system as primary. > > So the questions arises as to why do you want to use gas instead of > sprinklers? > > Craig L. Prahl, CET > Fire Protection > CH2MHILL > Lockwood Greene > 1500 International Drive > Spartanburg, SC 29304-0491 > Direct - 864.599.4102 > Fax - 864.599.8439 > CH2MHILL Extension 74102 > [email protected] > > > > -----Original Message----- > From: [email protected] [mailto: > [email protected]] On Behalf Of Craig > Leadbetter > Sent: Monday, May 13, 2013 1:56 PM > To: [email protected] > Subject: Extra Hazard storage > > Can an extra hazard storage facility be protected by a gas system or dry > chemical system? > > > > -- > Craig Leadbetter > Safeguard of Marquette > PO Box 116 > Marquette, MI 49855 > > (O) 906-475-9955 > (F) 906-475-5474 > (C) 906-362-5393 > > [email protected] > _______________________________________________ > Sprinklerforum mailing list > [email protected] > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > _______________________________________________ > Sprinklerforum mailing list > [email protected] > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > _______________________________________________ > Sprinklerforum mailing list > [email protected] > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > -- Craig Leadbetter Safeguard of Marquette PO Box 116 Marquette, MI 49855 (O) 906-475-9955 (F) 906-475-5474 (C) 906-362-5393 [email protected] _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org