Viking Fire Flex makes ICAF deluge systems. All open nozzles.

You might use AFFF foam water closed head at a suitable density.


Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
24400 Highland Rd rm 25, CLE 44143
216-621-8899
216-570-7030 Cell
WWW.ATCOfirepro.com

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Craig
Leadbetter
Sent: Monday, May 13, 2013 2:42 PM
To: [email protected]
Subject: Re: Extra Hazard storage

Art,

A foam system was acceptable per spec. Which manufacturer would I look at
for the system that you have used.




On Mon, May 13, 2013 at 2:39 PM, Art Tiroly <[email protected]> wrote:

> A foam/water system could reduce the water supply required. I had very 
> good success with Compressed air foam. This greatly reduced water 
> supply required.
>
>
> Arthur Tiroly
> ATCO Fire Protection Design
> Tiroly and Associates
> 24400 Highland Rd rm 25, CLE 44143
> 216-621-8899
> 216-570-7030 Cell
> WWW.ATCOfirepro.com
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of 
> Craig Leadbetter
> Sent: Monday, May 13, 2013 2:26 PM
> To: [email protected]
> Subject: Re: Extra Hazard storage
>
> The project is a Class IC storage facility storing lampricide in 5 
> gallon containers with rack storage that is 2400 sqft. With a required 
> .45/3000 plus 500 PGM for two hours the cost of the water supply is 
> going to outweigh the cost of the building.
>
> The site is remote and there is no municipal water available.   If I have
> done my research through NFPA 30 correctly we are looking at a tank 
> that is 200,000 gallons or more. Unfortunately the site has existing 
> buildings and the site plan does not allow the space for a 
> non-protected building
>
> I was just trying to come up with a reasonable costing fire protection 
> system although there may be nothing that is reasonable for this facility.
>
>
> On Mon, May 13, 2013 at 2:17 PM, <[email protected]> wrote:
>
> > Is it bigger than a breadbox?
> >
> > Dry chem. Is typically reserved for protecting areas inside equipment.
> >  Not occupied or potentially occupied spaces.
> >
> > For large areas there are so many problems with keeping the area 
> > tight to contain gas such as FM-200 that it would be virtually
impossible.
> > Also gas systems aren't going to suitable for every commodity.  And 
> > lastly, if the Codes require sprinkler protection, most AHJ's aren't 
> > going to go along with a gas only system as primary.
> >
> > So the questions arises as to why do you want to use gas instead of 
> > sprinklers?
> >
> > Craig L. Prahl, CET
> > Fire Protection
> > CH2MHILL
> > Lockwood Greene
> > 1500 International Drive
> > Spartanburg, SC  29304-0491
> > Direct - 864.599.4102
> > Fax - 864.599.8439
> > CH2MHILL Extension  74102
> > [email protected]
> >
> >
> >
> > -----Original Message-----
> > From: [email protected] [mailto:
> > [email protected]] On Behalf Of Craig 
> > Leadbetter
> > Sent: Monday, May 13, 2013 1:56 PM
> > To: [email protected]
> > Subject: Extra Hazard storage
> >
> > Can an extra hazard storage facility be protected by a gas system or 
> > dry chemical system?
> >
> >
> >
> > --
> > Craig Leadbetter
> > Safeguard of Marquette
> > PO Box 116
> > Marquette, MI 49855
> >
> > (O) 906-475-9955
> > (F) 906-475-5474
> > (C) 906-362-5393
> >
> > [email protected]
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
> > kl er.org _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
> > kl
> > er.org
> >
>
>
>
> --
> Craig Leadbetter
> Safeguard of Marquette
> PO Box 116
> Marquette, MI 49855
>
> (O) 906-475-9955
> (F) 906-475-5474
> (C) 906-362-5393
>
> [email protected]
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>
>
>
> -----
> No virus found in this message.
> Checked by AVG - www.avg.com
> Version: 2012.0.2241 / Virus Database: 3162/5820 - Release Date: 
> 05/13/13
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>



--
Craig Leadbetter
Safeguard of Marquette
PO Box 116
Marquette, MI 49855

(O) 906-475-9955
(F) 906-475-5474
(C) 906-362-5393

[email protected]
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2012.0.2241 / Virus Database: 3162/5820 - Release Date: 05/13/13

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to