A 4" pipe 40" long with a shutoff valve should flow 1500 gpm and provide a
smooth flow to pitot. 


Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
24400 Highland Rd rm 25, CLE 44143
216-621-8899
216-570-7030 Cell
WWW.ATCOfirepro.com

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Roland
Huggins
Sent: Monday, May 13, 2013 4:57 PM
To: [email protected]
Subject: Re: Forward Flow Testing of BFP's

The latest issue of Sprinkler Age has an article addressing how to calculate
the flow for exercising the BFP.  You certainly don't need six 2-1/2 hose
valves.  Approximately what pressure do you have at the riser when flowing
the system demand (without hose demand unless you have INSIDE hose
connections).

Roland

 
Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org





On May 13, 2013, at 12:45 PM, Ralphy Henderson <[email protected]>
wrote:

> I have an 8" riser with BFP with a system demand of 1500 gpm. I was 
> going to provide a test header consisting of (6) 2 1/2" hose valves 
> for the forward flow testing of the backflow preventor but then 
> starting wondering if there were any other means or devices out there 
> that could achieve the same flow? Fewer pieces would be nice. What are 
> you guys using out there?
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2012.0.2241 / Virus Database: 3162/5820 - Release Date: 05/13/13

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to