In traditional architectural terms a lintel is the piece between two vertical supports over a portal, so it could (and often is) used to describe the header span not only over doors but also windows.
SML -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Roland Huggins Sent: Monday, May 13, 2013 2:06 PM To: [email protected] Subject: Re: NFPA 13: 11.1.2 (separation between hazards) By definition, a lintel is a header above an opening in a wall. If a beam would suffice, a room with a beam is would be two compartments. We reasonable assume that a fuel package is not placed within a doorway (aka under the lintel). Roland Roland Huggins, PE - VP Engineering American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives Dallas, TX http://www.firesprinkler.org On May 13, 2013, at 10:55 AM, Ralphy Henderson <[email protected]> wrote: > But it doesn't say a wall... it says "a barrier or partition capable of delaying heat". Isn't the intent to basically have a compartment capable of containing the heat in one area and ensuring only the sprinklers in the compartment operate? In dealing w/ compartments it is acceptable to have openings into other areas as long as the minimum lintel depth is met. This beam is basically an 18" lintel separating the two areas. > > > _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler .org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org