There is a very specific definition in '13-13.3.16 for limited combustible. It involves very specific tests and very objective criteria. Don't say they can't use the plexi-glass. Ask for the appropriate test for whatever they use. Now I'm rather sure they won't be able to produce the test for plexi-glass. If the AHJ approves it anyway then it's a risk decision on the contractors part.
Chris Cahill, PE* Senior Fire Protection Engineer, Aviation & Facilities Group Burns & McDonnell 8201 Norman Center Drive Bloomington, MN 55437 Phone: 952.656.3652 Fax: 952.229.2923 [email protected] www.burnsmcd.com Proud to be one of FORTUNE's 100 Best Companies to Work For *Registered in: MN -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of A.P.Silva Sent: Monday, May 13, 2013 11:56 PM To: [email protected] Subject: baffles NFPA 13 requires baffles (between sprinklers) to be non-combustible or limited-combustible. The contractor has installed plexi-glass baffles, and claims that is what is normally used and has been approved on previous projects. Any comments? Tony _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org