Non-concur - You now have a combustible concealed space. Well, caveat of I don't know of a translucent panel that meets the definition for the exceptions. So which exception of '10-13-8.15.1 do you think it meets to eliminate the head?
I admit to being nit-picky, especially the smaller the sky-light. But I have seen 30' x 30' rooms with translucent panels in place of typical ACT. Not so nit-picky in those cases. Chris Cahill, PE* Senior Fire Protection Engineer, Aviation & Facilities Group Burns & McDonnell 8201 Norman Center Drive Bloomington, MN 55437 Phone: 952.656.3652 Fax: 952.229.2923 [email protected] www.burnsmcd.com Proud to be one of FORTUNE's 100 Best Companies to Work For *Registered in: MN -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Colin Taylor Sent: Wednesday, May 15, 2013 11:15 AM To: [email protected] Subject: Re: Skylights Mike You are correct. Regards Colin Taylor Sent from Samsung Mobile on O2 -------- Original message -------- From: Mike Hairfield <[email protected]> Date: To: [email protected] Subject: Skylights I have a project where the skylights are more than 32 sq.ft. in area which normally would require sprinkler protection, my project has a translucent panel attached at the roof line sealing off the skylight thus eliminating a ceiling pocket. My thoughts since there is not a ceiling pocket then sprinklers would not be required for this type of skylight. Any opinions? Mike Hairfield _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org Scanned by MailDefender - managed email security from intY - www.maildefender.net<http://www.maildefender.net> _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org